A customer has asked me to put in a supply for a sunbed in his house. He says it needs a 50amp single phase supply. So i was thinking putting in a 50amp c curve mcb from the fuse board which has a spare way fed in 10mm t+ e 10meters then into a rotary switch to the sunbed. The bed has not got an industrial plug. iv never wired a sunbed before, any thoughts? anyone dismantled one to get through the doorway?
thanks peeps
 
Sounds about right to me, just verify the watts the bed is pulling, then obviously choose the next size MCB up, (ie 50a what you mentioned may be okay, but cable calc it / cable derate just to be sure).

C curve should cope with inrush current, but as always with something like this manufacturers instructions are a must, then you are complying fully with the regs ;)
 
they have got an 80amp main fuse iv calculated diversity the 40% rule add up all the breakers x0.4 and it comes out at 76 amps do you think this is abit close ? would you recommend them upgrading to 100amp main fuse? Is this diversity rule acurate?
 
Last edited:
Even if there is a 80a cut out fuse the sun bed would have to be on for hours and hours th blow that fuse, i think they can take upto 5 x their badge rating, if there is only one sunbed in the house and not much else major (showers, et al) taking power that should be okay, anything else and its a call to the DNO for a cutout upgrade (sometimes free of charge depending on your area and state of the service head) or a get a 3 phase supply installed which isn't cheap i'm afraid matey.
 
they have got an 80amp main fuse iv calculated diversity the 40% rule add up all the breakers x0.4 and it comes out at 76 amps do you think this is abit close ? would you recommend them upgrading to 100amp main fuse? Is this diversity rule acurate?

i wouldn't rely on that calculation
 
they have got an 80amp main fuse iv calculated diversity the 40% rule add up all the breakers x0.4 and it comes out at 76 amps do you think this is abit close ? would you recommend them upgrading to 100amp main fuse? Is this diversity rule acurate?

The calculation is actually add up all but the largest breaker, multiply by 0.4 and then add on the largest.

This is only a rule of thumb mind. ;)
 

Reply to sunbed in house in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
620
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
954

Similar threads

Evening all, Just after a sense-check before I commit & send the quote. I’ve been asked to run in an SWA to feed a small CU that’ll sit inside...
Replies
0
Views
159
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top