Does anyone happen to know what "time interval expired (10223)" means on the the sunny explorer events log. It seems to happen at the same time every morning?? Many thanks in advance
 
Thanks for your help, perhaps i'll try to get a simple answer from sma. Atleast it doesnt appear to be a problem? Thanks again
 
You can stop this message from appearing by changing the following parameter:

Configuration of feed-in management
> Operating Mode Active Power change to Off

You will need a Gridguard code from SMA in order to make this change, after logging in as Installer
 
This is the answer that someone else received from SMA regarding this error code:

The message came up because inverter is waiting for a signal from the power reducer box and if it doesn’t sense that signal then it times out after awhile and then will work fine as usual. The reason that it didn’t show up before is because that device control feature isn’t available and is integrated on the new firmware hence causing that message to appear.
You can switch off that parameter manually using Sunny Explorer then this message won’t appear anymore. Please first login to Sunny Explorer as installer mode and then please go into Settings and click on the Equipment & device control system. Once the list have loaded, please click on the edit button at the end and find a parameter called Operating mode of feed-in management and use the drop down box to select it to OFF. This will then disable the feature that I’ve mentioned before and the error won’t appear anymore.


So it looks like there is some new functionality in the new firmware, but the feature is not present on the model of inverter, which is why it times out with the error.
 

Reply to Sunny exp information codes in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Hi Mainline and thanks for the reply. My inverter is only fed from the mains supply over a 4 hour period at night and it does not have any tie...
Replies
8
Views
2K
Yeah when we start up the cone crusher the power factor can drop from .9 to .5. I’ve seen it drop down to .4 during start up. We have more than...
Replies
5
Views
704

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top