@TPES Heres a quick overview, I'm assumimg you're a qualified sparks and will take the correct protective precautions..
Check the AC side and that there is power to the inverter, then switch it off (isolator Switch)
If there is no AC power to the inverter it will not work and will display a fault mesage. It has to be connected to the grid as the inverter monitors that and synchronises itself to it.
If you have AC power to the inverter, then check the DC side (be careful all the DC system is live)
Turn of the DC isolator, disconnect the two dc plugs from the inverter, and you want to do two tests, one Voc - the Open Circuit Voltage, so with a proper DC test meter connect it up to the two dc plugs (we have test leads with the proper plugs on) then close the DC breaker and as a quick guess (all dependant upon the module types and amount of sun) you should typically see a DC open circuit volt reading in the region of 40v x the # of panels (they are connected in series like a battery in a torch)
The second test to do is to open the DC Isolator, connect the 2 DC plugs together and using a DC Clamp meter, measure the Short Circuit Current (Isc) with the plugs connected and the ammeter in place close the DC isolator take the reading, open the isolator. You will get a current reading that is most dependant upon the amount of sun and the angle of the panels, it could be anything from 0 Amps at night to 6+amps in full sunlight.
If you've got voltage and current.
Put the DC plugs back on the inverter, close the DC Isolator, watch all the information that comes up on the inverter, Close the AC isolator.
It'll take about three minutes to synchronise with the grid before it starts generating.
You can download the Sunny Boy manual from the SMA Website
Home. SMA Solar Technology AG which will give you the fault codes