Hi Every One
Just need a bit of advice Please, what would you say the suply type is?? I cant fin a earth rod any where, customer says there isnt one Ze or Ra reading is 0.15 ohms pretty good for TT so I can only think its A TNCS but the earth is sperate??!!


Many Thanks

Any Help would be appricated (I'm stummped) P1010771.jpg
 
Most likely TN-S.
Your measured Zs is so low it's a most improbable Ra for TT.
It looks like the wrong head termination for TN-C-S, but measure PSCC and PEFC and if they're both the same you'll know it's actually TN-C-S and if different it's TN-S.
 
Last edited by a moderator:
If the earth goes into the ground then surely its TT. I would of thought that if it were TNS then the connection to the suppliy cable would of been made in the meter box.

Did you disconnect your main bond for the Ze. Only reason is on a CU swap that was TT with the bonds connected i had an RA of 0.19
 
Do a Ze on supply line & neutral.

That will help rule out TNCS which im sure it isnt.

After that, its a process of elimination and investigation, but its unusual to have a lead incommer with a spike.
 
Is it a 16mm E/Conductor? Hard to see whether its a 10 or 16mm. Only reason I ask is it could be a bonding cable giving you a false reading to earth? Just throwing it out there, as it does seem strange how theres no clamp near the cut out.
 
Hi Rob

The eath conductor seems bigger than 16mm when I offered up my sample 16mm, but I'm sure its not 25mm and as theres no inbetween size it must be 16mm??!!
Thanks for replying to my thread
 
As I'm still learning, can I just ask a couple of questions regarding this installation..

1. What is the purpose of the small black box right next to the service head? The one that looks like it is taking a feed from the live.
2. Why is there an earth cable going into the second meter?

Cheers
 

Reply to Suply Type ?? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
190
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
886
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top