D

Dave 85

Hi lads
Could someone please remind me of the requirements for supp bonding in a bathroom which has all circuits RCD protected, not got a regs book to hand.
Many Thanks
 
Hi lads
Could someone please remind me of the requirements for supp bonding in a bathroom which has all circuits RCD protected, not got a regs book to hand.
Many Thanks

Assuming the RCD has an operating current of 30mA and all circuits in the bathroom are protected there is no requirement for any supplementary bonding.

Also assume that your main equipotential bonding is up to scratch of course.
 
It is not the case that if RCD protection is in place you can ignore supplementary bonding. All extraneous conductive parts within the location must be effectively connected to main bonding in accordance with 411.3.1.2....this generally means a continuity reading <1667 ohms.
701.415.2

It's highly unlikely that a bath will be an ECP....the pipes supplying it probably will be,so it is the pipes which may require bonding,not the bath.
 
It is not the case that if RCD protection is in place you can ignore supplementary bonding. All extraneous conductive parts within the location must be effectively connected to main bonding in accordance with 411.3.1.2....this generally means a continuity reading <1667 ohms.
701.415.2

It's highly unlikely that a bath will be an ECP....the pipes supplying it probably will be,so it is the pipes which may require bonding,not the bath.


You are quite right I forgot to add the three requirements of 701.415.2 . This was a topic in a recent post that I included the reg numbers.
 

Reply to Supp bonding to a bath in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
701
  • Question
Bonding cables don't need to be insulated, other than for a short section at the end to identify them, and as long as they're 4mm2 or greater are...
Replies
1
Views
562

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top