Hi lads
Could someone please remind me of the requirements for supp bonding in a bathroom which has all circuits RCD protected, not got a regs book to hand.
Many Thanks
 
Hi lads
Could someone please remind me of the requirements for supp bonding in a bathroom which has all circuits RCD protected, not got a regs book to hand.
Many Thanks

Assuming the RCD has an operating current of 30mA and all circuits in the bathroom are protected there is no requirement for any supplementary bonding.

Also assume that your main equipotential bonding is up to scratch of course.
 
It is not the case that if RCD protection is in place you can ignore supplementary bonding. All extraneous conductive parts within the location must be effectively connected to main bonding in accordance with 411.3.1.2....this generally means a continuity reading <1667 ohms.
701.415.2

It's highly unlikely that a bath will be an ECP....the pipes supplying it probably will be,so it is the pipes which may require bonding,not the bath.
 
It is not the case that if RCD protection is in place you can ignore supplementary bonding. All extraneous conductive parts within the location must be effectively connected to main bonding in accordance with 411.3.1.2....this generally means a continuity reading <1667 ohms.
701.415.2

It's highly unlikely that a bath will be an ECP....the pipes supplying it probably will be,so it is the pipes which may require bonding,not the bath.


You are quite right I forgot to add the three requirements of 701.415.2 . This was a topic in a recent post that I included the reg numbers.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Supp bonding to a bath
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
Dave 85,
Last reply from
ruston,
Replies
11
Views
1,769

Advert

Back
Top