kingeri

-
Esteemed
Arms
Joined
Apr 13, 2012
Messages
2,598
Reaction score
1,346
Location
Yorkshire
8.5kw shower supplied by copper pipe......with plastic T where water supply branches to serve it, then back to copper. Any need to bond across the plastic T? Similar story with water supply to bath on hot and cold. All circuits RCD protected, shower itself earthed no problem.
 
the way to establish whether of not the copper after the plastic is extraneous is: IR test from the MET to the suspect pipework. if the reading is < 23Kohms, bond it. if it's> 23Kohms, don't. simplesss
 
Thanks guys. I already did the IR test this morning. I established in my own mind that it doesn't need bonding. The homeowner showed me under the floorboards on the landing and there are about 12 plastic Ts and elbows coming off copper. The plumber has bonded across them all....the homeowner said the plumber told her to make sure I do the same when I'm putting the shower in. I argued that it would probably not be necessary, but she gave me 'the look' (I don't trust you / you don't know what you're doing). The plumber has also used bits of 2.5mm T&E earth sleeved to do the 'bonding'. I have told her that even if it is established that bonding is necessary in a location, the stuff the plumber has used is totally wrong........ I'm going back after 5 o'clock. Can't wait.
 
Last edited:
Then start quoting her the regs, and what Tel said that you did a test and this and that, and basically tell her he is plumber, and you are the electrician, and you will even put on your certificate that you have IR tested the pipe it was ............ Kohms and therefore 230/ by your result gives you 0.0............. whatever milliamps and that will give you a touch voltage of ................ blah blah blah .......................let the plumber argue with that one
 
On a similar thread, I went to a job today where a customer had received an electric shock whilst in the shower. Its purely gravity fed, no electricity involved, but the mixer is metal and its fed by surface mount copper pipes that run up into the loft where they join plastic. As the water main is plastic there is no bonding. When he turned off the shower he received a shock and the rcd tripped. So my theory is some appliance in the house is introducing the current into the water, and because there is no bonding the rcd didn't trip until a naked man standing in water earthed it out. The fault wasn't present on arrival so I've temporarily bonded the pipes to the nearest socket, going back tomorrow to get involved. . . What I think I'm saying is, if in doubt bond it, then charge for the pleasure, everybody's happy!
 
some appliance in the house is introducing the current into the water,

can't see that, myself. clean water doesn't conduct.more likely an earth fault on an appliance to pipework. i'd test to see if there is any voltage present on the shower taps/pipes relative to the MET. ( with appliances switched on and off in turn)
 
Just got home from seeing the lady, I briefly explained the situation. She was happy with what I told her in the end. I did explain that there is a lot more to electrics than meets the eye....no disrespect to plumbers but you can usually see when a pipe is leaking.....it's not so obvious when you've got earth leakage etc. I suggested in future she let's a spark do her electrics.....including bonding! I did also make the point that I could have bonded at half a dozen points in her bathroom....and heck why not bond the kitchen sink too....and charged her for the pleasure.....but I didn't cos it was totally unnecessary!!!!
 
On a similar thread, I went to a job today where a customer had received an electric shock whilst in the shower. Its purely gravity fed, no electricity involved, but the mixer is metal and its fed by surface mount copper pipes that run up into the loft where they join plastic. As the water main is plastic there is no bonding. When he turned off the shower he received a shock and the rcd tripped. So my theory is some appliance in the house is introducing the current into the water, and because there is no bonding the rcd didn't trip until a naked man standing in water earthed it out. The fault wasn't present on arrival so I've temporarily bonded the pipes to the nearest socket, going back tomorrow to get involved. . . What I think I'm saying is, if in doubt bond it, then charge for the pleasure, everybody's happy!

Hasn't there been experiments done fairly recently that prove that clean (ie tap) water is an extremely poor conductor of electricity....especially over a distance.
 
yep. pure water ( can't say tap water is pure. more chemicals than ICI ) is not a conductor.
 
Dissolved conductive parts in water will be different from area to area in the UK, and that content can change almost on a daily basis. This is an old chestnut, but generally the harder the water the more conductive it will be.... I wouldn't trust any of the modern day water boards reports on there water supplies, most are just complete fabrications to cover there arse!! lol!!!
 
Oi! I made a lot of those chemicals!
Nothing wrong with them so long as you don’t drink the water. Beers a lot safer!

never a truer word has ever been spoken. i never drink water, you know what fish do in water!
 
Oi! I made a lot of those chemicals!
Nothing wrong with them so long as you don’t drink the water. Beers a lot safer!

never a truer word has ever been spoken. i never drink water, you know what fish do in water!
 
Back to the original problem, Re: bonding. If the customer wants it bonding and will pay, take the cowards way out, and just do it.

The customer is always right, misinformed and stupid, but always right!

The trouble is now your going to be bowing down the plumber’s knowledge!

Your in a no win situation.
 
Back to the original problem, Re: bonding. If the customer wants it bonding and will pay, take the cowards way out, and just do it.

The customer is always right, misinformed and stupid, but always right!

The trouble is now your going to be bowing down the plumber’s knowledge!

Your in a no win situation.

Tony, you're right, but I just like to have the last word where plumbers are concerned! :)
 

Reply to Supplementary bonding across plastic section of pipe in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
Replies
23
Views
2K
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
Replies
24
Views
1K
  • Article
This is an RSS feed of thread: Hole in copper pipe, solder under floor, T coupling & protection Content of the thread: I was stupid enough not to...
Replies
0
Views
117
  • Question
Ok. Thanks
Replies
6
Views
1K
C
  • Article
Noisy main cold water pipe, my plumber hasn't heard this before. Hi Folks, Would like to cast the net far and wide to try and get some resolution...
Replies
0
Views
133
ComfortablyNumb
C

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks