Sorry to ressurect a thread but i have just had a visit from building control and the building inspector said i have to cross bon the pipework to the basin in my ensuite?
This is a 4 bde 2 bath loft conversion which has been added and a new consumer fitted and all circuits tested by an electrician friend. I cross bonded the megaflow as a matter of course when i ran new earths to the water and gas mains.
I was under the impression that cross bonding in bathrooms was no longer required? The area she is looking at is inside a vanity unit that has no access once the granite top is fitted. I was also under the impression that it had to be visible?
I will bond it all in the eaves space to shut her up mainly but would just like to know 'the truth'
Thanks
Scott
As it's BC, I'll give you the answer from the good book, if you have a copy then take it along with you and show her the relevant parts when she is next on site.
Section 701, page 165 of BS 7671 concerns locations containg a bath or shower.
Regulation 701.415.2 covers supplementary bonding in the location and basically it says you must carry it out for any extraneous conductive parts entering the location unless
ALL of the following conditions are met.....
1. All main protective bonding (gas, water etc) is present and adequate.
2. All circuits of the location comply with the requirements for automstic disconnection in line with 411.3.2 (essentially in the event of a fault occuring the circuit will disconnect in less than 0.4s which it should if your electrician has tested & inspected it.
3. All the circuits within the location have additional protection via a 30mA RCD (again which they should if your electrician has inspected & tested it).
4. All the pipework within the location is effectively connected to the main protective bonding. There is a calculation for confirming this, ask your electrican to carry out the test and perform the calc for peace of mind if you like.
Sorry if the answer is a bit involved but it is from the book.
Essentially if all the main bonding is in place & there is the 30mA RCD protection to ALL the circuits in the bathroom, supp bonding can be omitted.