we are allowed to omit supplementary bonding on the 3 conditions (rcd, disconnection times and main bonding adequate )
if we have a plastic insert we may omit main bonding on water for example.
would supplementary bonding have to be added as it no longer has main bonding ?
 
Main protective bonding to the water service would not be required where the service enters into the installation in plastic or has a plastic insert then changes to copper.
Regulation 411.3.1.2 - Protective equipotential bonding:

Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding.
Supplementary bonding should not required in this instance but all circuits serving the location (assuming it’s a room containing a bath or shower) require additional protection by an rcd in accordance with 415.1.1
 
Last edited:
many thanks for the replies
i assume if it has a plastic pipe or insert it not considered an extraneous-conductive-part and is just a piece of metal?
 
If you are unsure if it's just a piece of metal or an extraneous conductive part you can I.R test. If it's greater than 0.02 MOHM then it's just a piece of metal.
 
If you are unsure if it's just a piece of metal or an extraneous conductive part you can I.R test. If it's greater than 0.02 MOHM then it's just a piece of metal.
But remember that this test will often show a connection to earth via boiler, immersion, water heater cpc's etc. And can send you down the route of thinking it's extraneous, when in actuality it may not be.
To get a true test you need to power off install and disconnect earthing conductor from MET and then test from piece of metal in question directly to earthing conductor.
 

Reply to supplementary bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
  • Question
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Replies
32
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top