Am I right in saying that back in the earlier edition of the regs, Supp Bonding was only required in bathrooms if the electrical accessory was in zone 1 2 or 3?
How would it be best described on a EICR then to say that it is present, can't be seen due to being boxed in but resistance between exposed conductive parts and extraneous conductive parts is low 0.03ohms.
When checking then, its aim is to keep possible touch voltage to <=50 volts.
If bonding has been carried out between extraneous parts, but not to the CPCs, but resistance between all extraneous parts and the CPC terminals of light, shower or what ever's installed give a resistance low enough to prevent voltage rising above 50v, is this acceptable?