Am I right in saying that back in the earlier edition of the regs, Supp Bonding was only required in bathrooms if the electrical accessory was in zone 1 2 or 3?
 
Am I right in saying that back in the earlier edition of the regs, Supp Bonding was only required in bathrooms if the electrical accessory was in zone 1 2 or 3?

In the 15th ed it was also a requirement in kitchens - I still think it should be, but then that could be regarded as contentious...

Its based on the fact that there were few MCBs (BS 3871)and more or less no RCDs (BS EN 61008) except for VOELBs and the occasional RCCB (BS4293) in TT systems. Fixed equipment had a maximum disconnection time of 5 seconds So you could be in a bath with an electric immersion heater right above you, a fault then developed which might last up to 5 seconds. Your only protection was/is in some cases, supplementary equipotential bonding, clamping the voltage rise to below 50V (touch voltage)
 
How would it be best described on a EICR then to say that it is present, can't be seen due to being boxed in but resistance between exposed conductive parts and extraneous conductive parts is low 0.03ohms.
 
How would it be best described on a EICR then to say that it is present, can't be seen due to being boxed in but resistance between exposed conductive parts and extraneous conductive parts is low 0.03ohms.

As long as it does what it was supposed to do then it cannot be said that it is unsafe. since it would be compliant with the 15th ed. However, it will not comply with he current regs, so it is likely to draw the C3 code and noted on the EICR.
 
We still supplementary bond our commercial type kitchens, communal dressing/shower rooms and even the domestic kitchens and bathrooms. But then ''All'' our kitchens are s/steel basins and or worktops and chromed copper waste pipes throughout!!
 
With the introduction of more and more plastic piping it’s about time it was brought back in to regular use.
Call me old fashioned if you like but it had it’s advantages. I’m sorry but I prefer “if it don’t move, bond it”.

Just hope the ex doesn't read this!
 
with 16th it was a req
with 17th it can be used as a means of providing additional protection
commercial kitchens still should have it
 
When checking then, its aim is to keep possible touch voltage to <=50 volts.

It works primarily for the old BS 3036 fuses where the 's/c' disconnection times for a current less than the minimum short circuit current to disconnect in < 0.4 secs since these are not as fast as MCBs. (0.1 or possibly as low as 0.01s) and will allow a certain amount of fault current through.

Zs <= 50 / Ia or more commonly appropriate to modern systems with RCDs as 50 / IAN.

You could, of course, use Ia in which case you would take the worst case which would be a fault on the largest item of equipment
 
If bonding has been carried out between extraneous parts, but not to the CPCs, but resistance between all extraneous parts and the CPC terminals of light, shower or what ever's installed give a resistance low enough to prevent voltage rising above 50v, is this acceptable?
 
Ah, now you are introducing a bonding zone that is not connected to the MET, which, if I recall makes it 'earth free'.
Now from 418, it becomes clear that this type of protection should only be installed under the supervision of trained personnel, that doesn't include domestic customers.

If there are metallic parts that are separated from an earth potential such as radiators supplied by plastic pipework, then I wouldn't connect them together.
 
Just trying to forget the existence of plastic piping for now and basing everything on copper pipework. Not many properties that i've come across that would have or need supp bonding sorting which have plastic plumbing.
 
If bonding has been carried out between extraneous parts, but not to the CPCs, but resistance between all extraneous parts and the CPC terminals of light, shower or what ever's installed give a resistance low enough to prevent voltage rising above 50v, is this acceptable?

Do you mean with a connection to the MET, but not to any CPC's or just between ECP's themselves?
 

Reply to Supplementry Bonding with previous edition regs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

I’d be more concerned about those blanking clips on the main CU.
Replies
24
Views
4K
Concerning isn't it. I fear it's just going to lead to reduction in standards and entry requirements and flood the industry with even more poor...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top