From ESQCR 2002
"SCHEDULE 2 Regulation 17(2)
MINIMUM HEIGHT ABOVE GROUND OF OVERHEAD LINES
Column 1 Column 2 Column 3
Nominal Voltages Over Roads Other Locations
Not exceeding 33,000 volts 5.8 metres 5.2 metres
Exceeding 33,000 volts but not exceeding 66,000 volts 6 metres 6 metres
Exceeding 66,000 volts but not exceeding 132,000 volts 6.7 metres 6.7 metres
Exceeding 132,000 volts but not exceeding 275,000 volts 7 metres 7 metres
Exceeding 275,000 volts but not exceeding 400,000 volts 7.3 metres 7.3 metres"
From ESQCR guidance notes, seems if insulated there is no specific clearance height.
"17(3)
This paragraph identifies three types of overhead line equipment that need not comply with Schedule 2, provided the equipment is not installed over a road:
(i) lines which are fully insulated (see definition of insulation at regulation 1(5));
(ii) exposed conductors connecting equipment (fixed to the support) to the line, provided the conductors are at least 4.3m above the ground (e.g. connections to pole mounted transformers or auto-reclosers); and
(iii) lines which are connected with earth, e.g. earth wires or neutral conductors on low voltage networks."
Regulation 1(5)
"insulation
This term defines insulation surrounding phase conductors which is designed to withstand the operating voltage of the equipment.
Insulation as defined does not include protective coverings or coatings (surrounding phase conductors) which are not designed to support the full phase to earth or phase to phase voltage (as appropriate). For example the covering on BLX overhead line conductors could not be described as insulation"