Supply for Combi Boiler - RCD required ? | on ElectriciansForums

Discuss Supply for Combi Boiler - RCD required ? in the UK Electrical Forum area at ElectriciansForums.net

Dave OCD

-
Mentor
Esteemed
Arms
Joined
May 5, 2015
Messages
4,158
Reaction score
7,261
Location
Cornwall
Allright chaps

I have to connect a new Combi this Saturday morning, intending to fit a 3 amp fused switched FCU and take the supply off a handy socket [about 2 feet away and on a RFC not a spur]

The consumer unit is an old MEM with cartridge fuses and there's no RCD, [TNCS system with Ze of 0.14]
Now assuming the owner doesn't want a new CU [yet anyway] would you be happy to connect up as is or would you fit an RCD spur ?
I have an opinion but just wondered what other people might think ?
 
My understanding is that any NEW work, which would include this, was required to comply with Current Regs. The regs only require that cable burried in walls etc be protected by an RCD, specifically surface wireing is not required to be RCD protected. so will there be any new wire passing through walls?
 
My understanding is that any NEW work, which would include this, was required to comply with Current Regs. The regs only require that cable burried in walls etc be protected by an RCD, specifically surface wireing is not required to be RCD protected. so will there be any new wire passing through walls?


not quite right. passing through walls don't need RCD. buried in the plaster < 2" deep does.
 
My understanding is that any NEW work, which would include this, was required to comply with Current Regs. The regs only require that cable burried in walls etc be protected by an RCD, specifically surface wireing is not required to be RCD protected. so will there be any new wire passing through walls?

Not in this case, it'll be about 2 feet of 0.75mm H/R flex from a fused spur right next to an existing socket.
 
My understanding is that any NEW work, which would include this, was required to comply with Current Regs. The regs only require that cable burried in walls etc be protected by an RCD, specifically surface wireing is not required to be RCD protected. so will there be any new wire passing through walls?
Well you tel that to my NICEIC inspector! In fact maybe the word "buried" might have more exactly expressed what I ment.
 
not quite right. passing through walls don't need RCD. buried in the plaster < 2" deep does.

So in that case an RCD is not strictly needed, but of course you will have checked that the supplementary bonding that was required by the previous standards to which the boiler was first installed are present!!! The problem being that if an earth fault developed then it would be to the boiler which is connected to the metal work of the water and the gas and these cannot be allowed to become live. So in the end it's your decision which way to go.
 
Last edited:

Reply to Supply for Combi Boiler - RCD required ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top