been to a job today where a seperate fuseboard has been fitted to supply an 8.5kw shower the supply and load cables for this board are 6.0mm twin and earth, the shower fuseboard has a 32a mcb and an rcd main switch and labelled up shower only, the feed for the seperate fuse board (only room for the one circuit) is 6mm twin and earth direct from the main Fuseboard incoming terminals is this ok ? The main fuse is 60a as the load is fixed at 32a and the 6mm cable is suitable for this the run between consumer units is surface mounted and double insulated less that 300mm long the only protection for the 6mm cable feeding the seperate fuseboard is the main fuse 60a no overloading of this cable is possible as the upstream 32a mcb restricts this the only issue would be a short circuit should the cable be damaged which with the PFC reading 1.2ka this is irrelevant isn't it ? Just wondering, Or have I misunderstood