hi
How can I find out ze and the supply fuses info at a factory installation for a certificate?
I cant turn all the factory off to disconnect and do a ze test and I cant remove the service head to see fuses.
The niceic have said that you should put not verified on the certificate or phone the supplier and ask them.
I have phoned Eon and they said they have no idea what the fuses are and can only say the Ze should be no higher than 0.8 for the tns supply.
I want to knowwhat others do in this situation ?
I have installed new circuits.
Answers please