You come to fill in the section of a PIR entitled "Supply Protective Device" but the supply protective device is sealed. Do you:

a) Break the seal to examin the device? (you are not allowed to break the seal!)

b) Take a guess, but in that case do you enter 60, 80 or 100 for the rated current?

c) Declare a limitation and just leave the section blank.

d) Waste time phoning the distributor (who probably doesn't know the answer anyway)
 
I have to agree with the first two replies re LIM, as a retired EEB inspector I can confirm that the carrier markings are not indicative of the fuse ratings, there are two size carriers smal and large, the small is normally 60A but could be 80A but no more, the larger carrier is normally 100A but we had fuses affectionally known as fat 60A and 80A which would be fitted at the inspectors discretion eg for 16.00 tails.

NB it is not illegal to break seals for safety or emergency reasons, only abstraction of electricity is illegal
 
Thanks, that's what I thought. Its just that my NICEIC inspector gave me the impression, without actually saying anything, that I should have done better than to declare a limitation.
 

Reply to Supply Protective Device in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
Yes, for example: https://kingsmillindustries.com/product/km2-20-10-sc/ However, the reality is the L-N-E style are far more useful in general as...
Replies
2
Views
970

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top