Inspection i did about two weeks ago and im going back to do the remedial work tomorrow, next to the main ccu there is a one module unit plus 61008 rcd main switch, inside the unit is a 32A MCB protecting an armoured outside supply, the module unit is fed by 6mm single spured of the incoming side of the main switch in the main ccu.

my query is - should the tails theoretically be 16mm to match the main 60amp cut out fuse as technically this is a supply split, or are the little 6mm tails protected by the 32A mcb only allowing that much current to flow?

I see a lot of this and wanted other peopled opinion on it, personally i always put in henleys and split it correctly

cheers
 
Reg 434.2.1 allows reduced conductor size up to 3m before the reduced protective device as long as a maze of other regs apply. Typically branches off a rising main supplying flats.

However in this situation I am with you and would put in proper tails.
 
That would only be safe if the amount of CCc of the cable was less than what the fuses in the sockets added upto. So for 2.5mm2 which can take 27a before derating, then you could only have 2 sockets max (2x13a= 26a). If you then plug more into them, then your relying on the 13a fuse to provide over current protection.
 

Reply to Supply tail query in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top