Supply to a 63A RCB | on ElectriciansForums

Discuss Supply to a 63A RCB in the DIY Electrical Advice area at ElectriciansForums.net

Joined
Oct 1, 2016
Messages
152
Reaction score
14
Location
North yorkshire
Hi

I need to put a 63A RCB 6 way weatherproof consumer unit ( Garage unit ) with 2x6A , 2x20A , 1x32A MCB's, in my workshop at my farm , now the supply to it, comes from the Main 83A 3 phase fuse box on the other side of the wall where I want to mount this unit , the length of cable would be around 500mm max .

Question , with it being such a short length of cable for the feed could I use a 6mm2 cable ! , as I have loads of it, but no 10mm2 .


cheers


spike
 
There is no ocpd on the supply , apart from the main 3 phase 83A 30mA RCD trip switch coming into the Farm , basicly I am wanting to know if a short length 400mm of 6mm2 cable will take the load of a 63 amp 30mA double pole RCD trip switch .
 
83A rcd is your protection??? So as this isnt an ocpd you must be relying on DNO for ocpd on this submain? i think you need rethink your design, whats the earthing arrangement.?
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.
 
Hi

Thanks for your feedback , the lights (lights 60W ) are only for the Tack room x1 and grain store x1 , chicken room x2 , the sockets are for these rooms only , they are part of the main workshop ( but they are separated ) it all was the Cow shed !.

The Main workshop wiring is fine ( off the blue phase ) , anyway what I have done is :

Have changed the Main supply fuse feeding the 63A RCD from 83A to a Lawson 63A ,( this is off the Yellow phase , house is off the Red phase ) and used a 10mm2 cable to supply the 63A RCD , yes I know I really should put in 16mm2 tails ! , needed it doing today

ps: I would not do anything until I was 100% sure it was right , that is why I am asking the questions , maybe stupid questions but if I get the correct answer at the end that is what I will do ! , not before .
I am not a Electrician as you have guessed , I am a time served mechanic so I do have a bit of savvy about me , not a lot but a bit ! , as they say in my trade you learn something everyday ! .

spike

Read more: Supply to a 63A RCB - http://www.diynot.com/diy/threads/supply-to-a-63a-rcb.467722/#ixzz4Ltk1uUJ4
 
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.
 
It would have been cheaper, safer and legal to have bought the right size cable.
Choosing to work illegally and unsafely for greater cost it not generally the best approach.
However you are unlikely to overload any parts with the set up as you have described.
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.

It is not fed direct from the DNO fuse , this feed come via a 63A RCD 30mA from the DNO fuse box ! .
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.


No not 6mm2 , I am using 10mm2 as I have just stated ! .
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.

It is not fed direct from the DNO fuse , this feed come via a 63A RCD 30mA from the DNO fuse box ! .
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.


No not 6mm2 , I am using 10mm2 as I have just stated ! .
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.

It is not fed direct from the DNO fuse , this feed come via a 63A RCD 30mA from the DNO fuse box ! .
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.


No not 6mm2 , I am using 10mm2 as I have just stated ! .
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.

It is not fed direct from the DNO fuse , this feed come via a 63A RCD 30mA from the DNO fuse box ! .
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.


No not 6mm2 , I am using 10mm2 as I have just stated ! .
 
The 63A 30mA RCD does not provide over current protection! You don't understand the basics...The thread should be closed before you burn the place down or kill some one.
 
Last edited:
Can you not post a picture of the setup, your explanation may be at odds with what is actually in place.
 

Reply to Supply to a 63A RCB in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

  • Question
Indeed. Sounds as though the only extra load is a 20 and a 6 breaker… could just be a light and a socket… or could just as likely be a dozen...
Replies
8
Views
681
dreadful, I couldn't sleep at night after that install, it may just about pass but the quality of work is substandard IMO
Replies
4
Views
472
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
658

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks