Supply to a one way CU for shower.. please help Hi guys I need some help if you would, I feel i should know this but I dont.
New shower going in, there is no provision/circuit existing for 9.5kW shower that is going to be installed.
I'm going to use a 30mA RCD + 45A MCB one way unit
Ive done the calcs, 6mm T&E should carry the current fine as its clipped direct in a loft with no insulation and not grouped, Vold drop will be 6v approx over 20m
My question is where do i feed the one way CU from?, do i use some of the 6mm and connect it to a protective device in the existing BS 3036 rewirable board?, there are only 30A max in there and although ive seen shared 3036's before, is it right?, or can i go into the outgoing side of the main switch?, im just wondering what will be protecting those 6mm tails?
New shower going in, there is no provision/circuit existing for 9.5kW shower that is going to be installed.
I'm going to use a 30mA RCD + 45A MCB one way unit
Ive done the calcs, 6mm T&E should carry the current fine as its clipped direct in a loft with no insulation and not grouped, Vold drop will be 6v approx over 20m
My question is where do i feed the one way CU from?, do i use some of the 6mm and connect it to a protective device in the existing BS 3036 rewirable board?, there are only 30A max in there and although ive seen shared 3036's before, is it right?, or can i go into the outgoing side of the main switch?, im just wondering what will be protecting those 6mm tails?