Supply to con unit? | on ElectriciansForums

Discuss Supply to con unit? in the Australia area at ElectriciansForums.net

I

ian t

Hello to all,
Could do with a spot of advice please.

Is it acceptable to utilise an existing 6mm T&E cable to supply a second consumer unit to be located in an extension, comprising a utility room and a wet room. The new con unit (clients requested) will supply a couple of double sockets, 3 lighting points, an outside socket, underfloor heating (11amps peak load) and a 24v transformer for a shower pump. The 6mm T&E is supplied from a 32amp MCB on the RCD side of existing con unit, and tests ok The second con unit will have split rcd protection (17th edition)
Are ther any implications to having 2 rcd's in line, one for 6mm cable and one for the final cicuit?

Thanks in advance
 
Not a good idea to have two 30ma rcd's in line.

Therefore the second location could be supplied from its existing RCD protected way and have a standard board with no rcd to achieve discrimination.

32Amp should be ok however, it is up to you to ensure that the supply will meet demand, being a utility room and wet room.

If its doable, i would try and get a 10mm in there with a 40A upfront.

IMHO.
 
your one at the main cons unit could be typeS time dalayed

Depending on how the 6mm T+E sub-main was installed i.e, if at a depth of less than 50mm from the surface of the wall then and not in earthed metallic conduit, it would need 30mA protection. If surface run in it's entireity in trunking/conduit and labelled etc then TD RCD would be ok.
 
Depending on how the 6mm T+E sub-main was installed i.e, if at a depth of less than 50mm from the surface of the wall then and not in earthed metallic conduit, it would need 30mA protection. If surface run in it's entireity in trunking/conduit and labelled etc then TD RCD would be ok.
wot,can you not get 30ma with a time delay?
 
Thanks folks, i think the 6mm will need putting on a separate RCD so it doesn't effect the main house in the event of tripping, but only the extension. I presume that would comply with 314, installation circuit arrangements?
 

Reply to Supply to con unit? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top