gregmac

hi

first post

i went to look at a job tonight. the isolator for the house is outside on the garage around 12metres away from cu. the supply needs changed as it is joined onto a 10mm t&e which isnt a pretty joint.

the house is a 3 bed bungalow. what size of swa would you recommened to run in? i was thinking of glanding it into an enclosure and having henley blocks inside it with 25mm tails coming out of it?

also i done a ze on the property at the isolator and there is on earth. which means i will need to make it a tt system.

i have never done an earth spike before as i am not long time served. i was going to put the spike outside the property in an appropriate enclosure.. what size of earth from the spike to the cu would i need to run?
#
could someone give me some advicde on how they would tackle this please

would be much appreciated
 
16mm earth ,use threaded earth rod so you can get down deep as the standard 1 metre ones are not usually long enough,also you can buy a special earth rod pit made by Furse, which is like a stop tap cover only a bit bigger.Watch out for buried services when driving the rod in.
 
16mm earth ,use threaded earth rod so you can get down deep as the standard 1 metre ones are not usually long enough,also you can buy a special earth rod pit made by Furse, which is like a stop tap cover only a bit bigger.Watch out for buried services when driving the rod in.

Will do thanks for response. Any suggestions on the suplly i was on about
 
if the DNO fuse is 100A, use 25mm. if 80A or 60A, you can yse 16mm. switch fuse required within 3m of service head if tails over 3m. earthing conductor to rod needs to be 6mm or over.
 
if the DNO fuse is 100A, use 25mm. if 80A or 60A, you can yse 16mm. switch fuse required within 3m of service head if tails over 3m. earthing conductor to rod needs to be 6mm or over.



Would urecommened glanding into am enclosure at both cu and dno isolator side joining armour into henley blocks with 25mm tails coming out or...
 
Before you start driving in rods and creating a TT system, give your local DNO a call to find out if your local DNO supply has been PM'Ed!!

If your out of luck with the PME. ...As suggested earlier, use 5/8'' extendable rods and use at the very least 2 of them coupled together for depth and system stability. Don't drive rods within a metre of external walls, as you will hit all the old builders rubble. Also as suggested earlier use a flush to ground earth pit box, which will protect your rod and connection and also give a means
of visual location for the future...
 

Reply to supply to house in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
288
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
945
  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
  • Question
No, that is part of a different earthing system, don't mix the different earthing systems unless you have given proper engineering consideration...
2
Replies
27
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks