Hi all, I’m new to this forum so please bare with me.
I was after some advice if possible, I’m going to be taking a supply to a log cabin in a customers garden and wiring the log cabin itself. The cabin is pretty much a small bungalow with shower,cooker,hob,ring,water heater,lights and an electric heater so as you can imagine the max demand load will be pretty high. Il be running the cables externally in plastic conduit to allow for expansion of the cabin.
Am I right in taking a supply from the Origin via an 100A DP switch with an 80A HRC fuse. Run in 25mm SWA to allow for voltage drop (approx 35m run). Supplying either a split load board or individual Rcbo’s.
In terms of earthing am I right in thinking if the origin is TNS I can use the earth contained in the SWA and if its TNCS I’d have to install a rod and TT the system at the log cabin.
Does the swa from the origin need rcd protection?
Any tips that may come in handy when working the log cabin?
Thanks I’m advance.
I was after some advice if possible, I’m going to be taking a supply to a log cabin in a customers garden and wiring the log cabin itself. The cabin is pretty much a small bungalow with shower,cooker,hob,ring,water heater,lights and an electric heater so as you can imagine the max demand load will be pretty high. Il be running the cables externally in plastic conduit to allow for expansion of the cabin.
Am I right in taking a supply from the Origin via an 100A DP switch with an 80A HRC fuse. Run in 25mm SWA to allow for voltage drop (approx 35m run). Supplying either a split load board or individual Rcbo’s.
In terms of earthing am I right in thinking if the origin is TNS I can use the earth contained in the SWA and if its TNCS I’d have to install a rod and TT the system at the log cabin.
Does the swa from the origin need rcd protection?
Any tips that may come in handy when working the log cabin?
Thanks I’m advance.