I have run a 2.5mm 3 core armoured cable from my cu in the house connected to a 16 amp cb on the rcd side of the cu. this runs approx 20m to the garage and is connected to 4 double sockets and a fused connection unit to 2 flouresent tubes. The sockets rarely power more than 2 items and Zs is below way below 2.87ohms. is it ok like this or does the garage require its own cu?
I have used the 3rd conductor as the earth but i have connected the armour and the terminal boxes at either end to the MET also the Zs was checked b4 i connected the armouring.
I cant remeber the exact figure of Zs now ( idont think it was over 1 ohm, my Ze is 0.21, i have a TN-C-S supply ) and i can find the note pad i wrote it down on, i thing the missus used it as a phookin shopping list.
Thanks
I have used the 3rd conductor as the earth but i have connected the armour and the terminal boxes at either end to the MET also the Zs was checked b4 i connected the armouring.
I cant remeber the exact figure of Zs now ( idont think it was over 1 ohm, my Ze is 0.21, i have a TN-C-S supply ) and i can find the note pad i wrote it down on, i thing the missus used it as a phookin shopping list.