I have run a 2.5mm 3 core armoured cable from my cu in the house connected to a 16 amp cb on the rcd side of the cu. this runs approx 20m to the garage and is connected to 4 double sockets and a fused connection unit to 2 flouresent tubes. The sockets rarely power more than 2 items and Zs is below way below 2.87ohms. is it ok like this or does the garage require its own cu?

I have used the 3rd conductor as the earth but i have connected the armour and the terminal boxes at either end to the MET also the Zs was checked b4 i connected the armouring.
I cant remeber the exact figure of Zs now ( idont think it was over 1 ohm, my Ze is 0.21, i have a TN-C-S supply ) and i can find the note pad i wrote it down on, i thing the missus used it as a phookin shopping list.

Thanks
 
Sounds fine to me too, ideally yo could have put a little 2way db with rcd main switch in the garage and covered sub main with time delay rcd to prevent nuisance tripping in the house if there's a fault in the garage as tel says
that would be for TT though dan.....dont forget that the earthing arrangement here is TN-C-S....and the garage feed is using an earthed mettalic covering (armoured)....so best to RCD it at the garage end (sub board)....just feed the armoured of an MCB on an unprotected way in the house C/U
 
Thank you all for your replies

The reason i did it this way was to keep the circuit a radial circiut part of the house installation as apposed to the swa cable being a supply cable, or does this not make any difference except reg 411.3.2.3 on page 47 in the red book.

Havent shelled out an a green one yet !!
 

Reply to supply to my garage in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
798
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top