Hi folks,
Rural domestic property with 2 outbuildings. TN-C-S with additional earth rod (believe was upgraded to underground TN-C-S feed from old overhead TT feed and rod was left in place). Main house has the only RCD (30mA) in the whole property as the main switch and there is much nuisance tripping. After testing and a lot of trial and error there is believed to be several causes of nuisance RCD tripping. Currently the outbuildings are each fed from an MCB in the main board over SWA to a sub board with several MCBs. I've proposed a gold standard upgrade to the client which he is keen on but not just yet (c. £1,200) and wants a more cost effective approach tried first. One of the outbuildings is believed to be a major contributor to the nuisance tripping. What I could do is redirect the feed to the suspect outbuilding to the external meter cupboard via a Henley block and take a feed directly from the meter to the outbuilding (this is easily done). The SWA to the outbuilding appears to have been correctly installed, but is under a tiled garden patio the whole way, with about 12 inches visible up an external wall to a junction box, and about 3 feet up a wall inside the outbuilding to a sub board. I do not know if the SWA has been installed to a suitable depth, irrespective of the fact that it's now covered by patio.
What I want to do is upgrade the sub board in the outbuilding to several RCBOs (it's a home office with a lot of IT equipment so hence the division of circuits to tackle relatively large residual current - this is one of the suspected reasons for tripping), but the question is what am I required to do by way of protection of the SWA cable. I've got a few options but I'm stuck on whether I need to be mindful of the rural nature of the property (hence why option a is included):
(a) a DP 100mA time delayed RCD in the meter cupboard, or
(b) a DP main switch with an MCB for overcurrent protection of the SWA, or
(c) just a DP isolator in view of the well covered nature of the SWA with only a little on show. I can easily protect the exposed SWA using external capping.
Thanks loads! SW
ps. Please no input about reasons for nuisance RCD tripping or earthing for the outbuilding; well across that thanks.
Rural domestic property with 2 outbuildings. TN-C-S with additional earth rod (believe was upgraded to underground TN-C-S feed from old overhead TT feed and rod was left in place). Main house has the only RCD (30mA) in the whole property as the main switch and there is much nuisance tripping. After testing and a lot of trial and error there is believed to be several causes of nuisance RCD tripping. Currently the outbuildings are each fed from an MCB in the main board over SWA to a sub board with several MCBs. I've proposed a gold standard upgrade to the client which he is keen on but not just yet (c. £1,200) and wants a more cost effective approach tried first. One of the outbuildings is believed to be a major contributor to the nuisance tripping. What I could do is redirect the feed to the suspect outbuilding to the external meter cupboard via a Henley block and take a feed directly from the meter to the outbuilding (this is easily done). The SWA to the outbuilding appears to have been correctly installed, but is under a tiled garden patio the whole way, with about 12 inches visible up an external wall to a junction box, and about 3 feet up a wall inside the outbuilding to a sub board. I do not know if the SWA has been installed to a suitable depth, irrespective of the fact that it's now covered by patio.
What I want to do is upgrade the sub board in the outbuilding to several RCBOs (it's a home office with a lot of IT equipment so hence the division of circuits to tackle relatively large residual current - this is one of the suspected reasons for tripping), but the question is what am I required to do by way of protection of the SWA cable. I've got a few options but I'm stuck on whether I need to be mindful of the rural nature of the property (hence why option a is included):
(a) a DP 100mA time delayed RCD in the meter cupboard, or
(b) a DP main switch with an MCB for overcurrent protection of the SWA, or
(c) just a DP isolator in view of the well covered nature of the SWA with only a little on show. I can easily protect the exposed SWA using external capping.
Thanks loads! SW
ps. Please no input about reasons for nuisance RCD tripping or earthing for the outbuilding; well across that thanks.