jibjob

-
Arms
Joined
Mar 13, 2009
Messages
133
Reaction score
17
Location
Cheltenham
Hi all,

A local restaurant has been having problems with intermittent tripping of RCBO supplying a metal shipping container which they use for storing frozen food etc. I've identified the fault which I won't go into as it's not really relevant.
The system is TT, & currently there is 4mm SWA running to the container from the CU protected by a single pole 32a RCBO with a DP main switch isolator up front (as opposed to a time delay RCD).
The SWA emerges from the ground about 6" from the edge of container, goes underneath it & appears at the rear of the container in 2.5mm T&E (don't ask) which then passes through the container by means of what looks like some sort of ventilation duct to a metal clad CU which bizzarely has been mounted upside down.
Two circuits to lights & sockets, T&E cable haphazardly draped around the container, no main bonding, all n all a total mess.
I've proposed to break into the exising SWA where it emerges from the ground, not sure whether I'll joint it under or overground yet, it will depend on how much cable I have to play with & continue to CU in SWA around the outside of the container to CU. Will install main bonding & rewire the container in PVC conduit & metal clad accessories.
I was thinking that I should also sink a spike local to the container (container is approx 25m from main building) & stick a 100mA time delay RCD on the front of the main board in main building. All circuits on main board have 30mA protection by means of single pole RCBOs.
Any thoughts would be most appreciated

Cheers:)
 
Hi all,

A local restaurant has been having problems with intermittent tripping of RCBO supplying a metal shipping container which they use for storing frozen food etc. I've identified the fault which I won't go into as it's not really relevant.
The system is TT, & currently there is 4mm SWA running to the container from the CU protected by a single pole 32a RCBO with a DP main switch isolator up front (as opposed to a time delay RCD).
The SWA emerges from the ground about 6" from the edge of container, goes underneath it & appears at the rear of the container in 2.5mm T&E (don't ask) which then passes through the container by means of what looks like some sort of ventilation duct to a metal clad CU which bizzarely has been mounted upside down.
Two circuits to lights & sockets, T&E cable haphazardly draped around the container, no main bonding, all n all a total mess.
I've proposed to break into the exising SWA where it emerges from the ground, not sure whether I'll joint it under or overground yet, it will depend on how much cable I have to play with & continue to CU in SWA around the outside of the container to CU. Will install main bonding & rewire the container in PVC conduit & metal clad accessories.
I was thinking that I should also sink a spike local to the container (container is approx 25m from main building) & stick a 100mA time delay RCD on the front of the main board in main building. All circuits on main board have 30mA protection by means of single pole RCBOs.
Any thoughts would be most appreciated

Cheers:)

Dont need rcd/rcbo upfront for swa.

Get rid and have one inside unit
 
It sounds a complete mess regardless, no RCD time delayed main switch, all circuits fed from SP RCBOs. The SWA still feeding said container still needs to be RCD/RCBO protected. With all,sub circuits in the container then just needing to be fed via a normal main switch and MCBs.
 
It is a complete mess & in some ways I wish I'd never laid eyes on it. However, with a bit of work it can be sorted. My main concern is whether to put in another spike adjacent to container going back to sub board or whether to rely on the existing spike (Ra was 75ohms at main board).
 

Reply to Supply to shipping container in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Ask your electrician when they do a site visit as to what is required they can also notify the installation to Building Control under Part P of...
Replies
1
Views
383
Is the property suitable for ASHP? There are quite a few unscrupulous salesmen promising all sorts, but without the insulation factors and large...
Replies
9
Views
530
  • Question
Yes it will almost certainly be TNS if it has a direct feed from a substation.
Replies
9
Views
2K
davesparks
D
Not neccessarily. Bonding it may mean you are actually introducing a fault-path. We test to ascertain whether it is extraneous and whether it is...
Replies
17
Views
3K
Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
899

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks