A Happy, Healthy and Prosperous New Year to all of you.
Let the battle resume!
Customer has changed his mind. I was supplying a built in Double oven off a 6mmsq 32Amp protected radial and a built in microwave off a 13 Amp spur on the ring.
He now has two identical self cleaning ovens each requiring a 15 Amp supply. So no fused spur.
I know I'm permitted to connect the two ovens to one supply. My 6mm cable terminates in an isolator below the ovens. But the ovens (NEF) have 16Amp plug/socket connectors on them and are provided with their own dedicated flex and 16Amp connector. There is no way I can run 6mm into the ovens.
So I will have to reduce from 6mm to whatever size the flex is (looks like 1.5 mmsq).
Is this permitted?
If not, what do you suggest as a solution?
Cheers
Pete