I am busy doing some work with a local contractor to get some up to date hands on experience.
whilst doing a EICR today i come across a CU with SPD in. The property is a recently built 5th floor flat about to be let on a new tenancy and meets the criteria for requiring a SPD. The whole set up is all Hager products.
Having only briefly come across these before and never been involved in installing one I am a little unsure of the method.
i have gone and looked on Hagers site. They suggest both the 32A MCB and SPD should go in the CU after the 2 pole isolation switch but before the RCD's and other circuits.
Hager - Surge Protection Kit Videos - http://www.hager.co.uk/product-catalogue/energy-distribution/protection-devices/surge-protection-kits/videos/52326.htm
The installation I came across has the 32A MCB immediately after the isolation but the main SPD is at the end of the CU after all the circuits.
I have enclosed a picture, its is not too clear as the camera flash created shadows in the cupboard, but i have highlighted the relevant parts with Red arrows.
Can somebody tell me if this is the correct or acceptable method of installation or should it be installed as per Hagers own video? Surely, the SPD needs to go before all circuits otherwise damage would potentially be done to circuits before reaching the SPD?
Finally,Other than the green life indicator built into the SPD how do you test one? The company I am doing some experience with simply said if its green you are happy if its red change it.
Any advice would be appreciated. As i am led to believe these things are becoming more common, especially in new installs.
View attachment 35959
whilst doing a EICR today i come across a CU with SPD in. The property is a recently built 5th floor flat about to be let on a new tenancy and meets the criteria for requiring a SPD. The whole set up is all Hager products.
Having only briefly come across these before and never been involved in installing one I am a little unsure of the method.
i have gone and looked on Hagers site. They suggest both the 32A MCB and SPD should go in the CU after the 2 pole isolation switch but before the RCD's and other circuits.
Hager - Surge Protection Kit Videos - http://www.hager.co.uk/product-catalogue/energy-distribution/protection-devices/surge-protection-kits/videos/52326.htm
The installation I came across has the 32A MCB immediately after the isolation but the main SPD is at the end of the CU after all the circuits.
I have enclosed a picture, its is not too clear as the camera flash created shadows in the cupboard, but i have highlighted the relevant parts with Red arrows.
Can somebody tell me if this is the correct or acceptable method of installation or should it be installed as per Hagers own video? Surely, the SPD needs to go before all circuits otherwise damage would potentially be done to circuits before reaching the SPD?
Finally,Other than the green life indicator built into the SPD how do you test one? The company I am doing some experience with simply said if its green you are happy if its red change it.
Any advice would be appreciated. As i am led to believe these things are becoming more common, especially in new installs.