Can anyone tell me if its a requirement to install a surge protection device to a sub Distribution Board if it serves external equipment ie a roof mounted extract fan even though a SPD is located on the Main Panel?


Sent from my iPhone using Tapatalk
 
Your risk assessment will tell you whether surge protection is required and at what level.
A SPD at a main incomer will be rated differently than one at a final distribution point.
If you need accurate surge protection at an accessory then the overvoltage protection would operate at a significantly lower voltage than for a main incomer.

If you are protecting against lightning side strikes then this is not required in the UK as the risk is deemed to be low, however if equipment or services need resilience then it may be that SPD are needed.
 
The UK has <25 thunderstorm days per year and with the calculations in section 443 this equates to no requirement for SPD.
however if there is for example a key public service, bank server, medical system that requires continuous operation and must be protected from being be destroyed by a strike then it may be required to have spd protection.
 

Reply to Surge Protection Device in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

  • Question
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct...
Replies
7
Views
946
  • Question
Thank you for the advice; I did figure it would be in the realms of discovering, say, a 10mm earth cable in a property, and having no more...
Replies
2
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top