Hi guys, could someone help with the following please? The scenario is:

Domestic property supplied via three phase (with a 3P main DB, NO SPD).
Tails split via henley blocks, and a second single phase DB installed; this DB has an SPD for it and it's circuits.

Now, normally with a single phase property, if the first DB had no SPD but the second DB was fitted within 10M of it, the installation as a whole could be regarded as protected, and that would be that. However, in this case, as the SP DB is more than 10M away from the main 3P board, only the circuits in my board are protected. However, is there a requirement that I should also install a three phase (Type 1) SPD in the main 3P board, in order to protect the circuits supplied by that board too, or is my responsibility only actually limited to the DB I installed? Many thanks in advance for any advice!
 
If you have only installed the board with the SPD your remit stops there. Imagine a site with hundreds of boards, where do you draw the line.
Thank you for the advice; I did figure it would be in the realms of discovering, say, a 10mm earth cable in a property, and having no more responsibility for that, other than to recommend that it's upgraded to 16mm. I just wanted to check if this situation was any different, so cheers for the response.
 

Reply to Surge Protective Devices in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct...
Replies
7
Views
948
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top