Went to look at wiring a biomass boiler today ...

boiler and buffer tank located in a breeze block out building sat on concrete pad .

PME earthing system , existing supply to outbuilding in 25mm 3core swa .

ALL the pipework was in place (copper and steel pipe) connecting buffer tank and boiler .

Mains water also in place in nice blue plastic pipe .

Grabbed the wander lead and tester out of the van to test if the metal pipework was extraneous
and low and behold got a dead short . also dead short from unistrut on walls to earth (which is bizarre as
it is not in contact with anything metal) .
:rolleyes4:

So does concrete conduct electricity ? this is the only plausible answer .

i meggared between the concrete pad and earth at 500v with 32Mo resistance , so not conducting well !.

the buffer tank is 3000 litre and has a large metal footprint sat on the concrete pad .


im going to bond the pipework but am gobsmacked as to how it has become an extraneous part .



your thoughts on this please .
 
When you say 'dead short' was that on the insulation resistance range?

On my tester (Fluke) anything below 20K is shown as '0' on the insulation test range. Change to continuity test to see if it is really a dead short!
 
yes on insulation resistance at 500v and 250v , hmmmm its a fluke 1653b aswell .

didnt know that yellowvanman , was showing 0.00 Mo but in the bottom right corner

of the tester shows the voltage gone through i think ? this was coming back as 1 volt ?

so im not sure whats going on with that ?

Changed over to continuity but cant seem to remember what the reading was , i will retest

tomoro and take my old megger .


i did notice the walls were damp DILLB but the pipe clips attached to the strut are insulated .


If it is below 20k it needs bonding
 
If there's copper and steel pipework and I'm guessing mostly metallic boiler there might be motivation to bond to reduce corrosion regardless of whether the components test as extraneous conductive or just exposed conductive.
 
You mention the mains water was in plastic pipe but what about other outgoing pipe connections to the building it serves?

Moisture-laden concrete is conductive enough that if (say) a rawlbolt holding the tank framework is touching a rebar grid in the slab it could give you quite a low reading, due to the large area of metal in intimate contact with the concrete. You probably won't get any reading by probing the surface because the contact area is so tiny and the screed will probably be drier anyway.
 
wouldnt class them as an exposed conductive part marvo .

will do some more testing tomoro but will likely be bonding .

cant get my head around the earth path though .

Think about what a Ufer earth is, and you will see that concrete (depending on it's make-up) that incorporates a metal rebar grid can be a good conductor, especially when in contact with perpetually damp or wet ground....
 
Concrete never actually dries out completely and is one of the best floor surfaces for conducting electricity which is one of the reasons they often put rubber matting in switch rooms,its actually one of the worst things you could stand on if you happen to get an electric shock.
 
Concrete never actually dries out completely and is one of the best floor surfaces for conducting electricity which is one of the reasons they often put rubber matting in switch rooms,its actually one of the worst things you could stand on if you happen to get an electric shock.

2nd worst, the worst thing to stand on would be one of Eng's earth rods! Daz
 
You mention the mains water was in plastic pipe but what about other outgoing pipe connections to the building it serves?

hello Lucien . all outgoing district heating pipes are insulated plastic .

I see the logic behind the large surface area of the buffer tank in contact with the concrete .
Todays test with the low ohm meter came back at 1100 ohms .

I have bonded the pipework and may suggest a rubber matting or insulator on the next jobs .

:cool3:thankyou for everyones help .
 
I didn't think you could transport PME supply I have a few times as there is no registration to say you can't a load of old ###### to me.

- - - Updated - - -

Regulation I meant predictive text for ya
 

Reply to Surprised by todays readings in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
404
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
993
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top