Hi - Can anyone help - I have a 3.67kw installation made up of 15 Sharp type ND-R245A5 panels in 2 strings ( 1 x 8 & 1 x 7 )
The inverter is a Sunny Boy SB3000 HF -30 which I was told was needed because of the uneven strings
Is this inverter powerfull enough to support a 3.67kw system as it seems never to produce above 2.9kw ?
Will it never achieve the annual 3.2 kw stated
 
Are you sure it is an SB3000 HF? If so, it only has a single MPPT and therefore it is not a good idea to have uneven strings connected to it.
 
What is tha orientation of the roof? south, east west split?
What is your location in the UK? what is the slope of your roof? (roughly in degrees)
 
Hi - Can anyone help - I have a 3.67kw installation made up of 15 Sharp type ND-R245A5 panels in 2 strings ( 1 x 8 & 1 x 7 )
The inverter is a Sunny Boy SB3000 HF -30 which I was told was needed because of the uneven strings
Is this inverter powerfull enough to support a 3.67kw system as it seems never to produce above 2.9kw ?
Will it never achieve the annual 3.2 kw stated
The only reason for using the 3000HF would be if it was run in single string, as the HF has a higher voltage range than most.

It's right at the top of the allowable input for the 3000HF, but that's not necessarily a bad thing, as the HF inverters are most efficient at high inputs, so while it will limit the output a little in full sun, it will probably generate more on average across the year.

Can you confirm how many of the PV cables you have going in to the bottom of the inverter - bottom left? Should be 2 cables if single string, 4 cables if 2 string.
 
Are you sure it is an SB3000 HF? If so, it only has a single MPPT and therefore it is not a good idea to have uneven strings connected to it.

Hi
Thanks for quick response.
It is definitely an SB3000 HF
Am I getting confused and it is not 2 strings but 1 and they had to use the HF because of 8 panels and 7 panels array
 
I have just checked and there are 2 cables going in the Inverter (bottom Left)
If it is 1 string did they have to use the HF because on uneven number of panels?
 
Could you provide a photo of the inverter? Do you have one or two DC isolators? They are normally grey on/off rotary-style switches. Especially interested in the connections at the bottom of the inverter and the wiring to the DC isolator(s).

Edit,

Just seen your post. Sounds like you have just the one string.
 
Last edited:
When you say that you have different strings, are they mounted on the same roof space? Or on a different roof space at a different orientation?

I would personally say that the 3000HF is not a bad choice for this array assuming that the panels are all at the same orientation. It may seem undersized but this is generally what installers do in the British climate - the basic understanding is that a 3000HF inverter will run better at, say, 2900w than a 3.6kW inverter - and that 2900w is far more common than 3.5kW. Does that make sense?
 
Same roof space - 1 row of 7 above a row of 8 all south facing on a roof with 30 degree pitch
I think I understand but will the gain by running better at 2900w outweigh the loss of never achieving above 3000w
 
Same roof space - 1 row of 7 above a row of 8 all south facing on a roof with 30 degree pitch
I think I understand but will the gain by running better at 2900w outweigh the loss of never achieving above 3000w

As far as my computer simulations go, it appears so.
 
[ElectriciansForums.net] Suuny Boy inverter SB3000 HF-30

Ok. Here's Philip's photo. Any comments? Looks pretty neat except for a possibly peeling label?
Looks like a single string as well.
 
Thanks that is good news.
However does this mean that the average annual system output will be less than the 3159 quoted and more like 2900
 
I'd expect your system to perform much better than 2900kWh per year. 3159kWh is the official Government SAP figure which tends to be rather pessimistic in my experience. You should do a bit better than that (assuming reasonable weather conditions of course).

I think your installer's done a decent job and hasn't "fiddled the figures".

You do have polycrystalline panels which are a bit less efficient than monos but they should work fine if installed correctly.
 
Last edited:
Thanks that is good news.
However does this mean that the average annual system output will be less than the 3159 quoted and more like 2900
no, I think you're getting mixed up.

the annual output is in kWh, whereas the limit on your inverter output is in kW.

They essentially are unrelated, though it roughly works out at around 8-900kWh per year per kWp of solar PV installed, which in this instance results in an annual output prediction of 3200kWh.

I'm not running this through sunny design as I've done this so many times I already know that the impact of the inverter being marginally lower rated than the peak output of the panels will result in losses of approximately 0.1-0.2% per year from the inverter capping the peak output, but the improved efficiency from running the inverter closer to it's peak efficiency point through the year should result in something like a 0.4-0.6% improvement in output, so the net effect is a marginally improved output.

3200kWh per year seems reasonable to me for a south facing system of this size, so I'd be reasonably confident that you should achieve this or thereabouts.
 
That number of panels in one string would produce an over voltage for the 3000HF. You would have to wire for two strings to keep the voltage within the operational range. This can be done by wiring the two strings directly back to the two string inputs on the inverter (still only one MPPT though). Alternatively the two strings could be wired together with connecting sockets on the roof and a single connection will then go to the inverter. I believe that in either case that the two strings should be the same size, orientation shading etc.
 

Reply to Suuny Boy inverter SB3000 HF-30 in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Connecting the inverters in parallel does not guarantee that the electrical circuit will see the circuit as parallel. Path of least resistance
Replies
2
Views
1K
Hi Again I have got the capacity set to 9600w/200Ah already on the bms and the only thing I have adjusted is the max charge at 50 amps on the...
Replies
4
Views
2K
There are a few choices, one way or another it will connect at 240V AC into your house wiring system. It really depends where the panel is wrt...
Replies
13
Views
3K
T
Hehe yeah MY PLANET SOLAR i have a better story than that which spans millions and a particular old conman. It took me months to ruin this one...
2
Replies
32
Views
6K
akaPABLO
A
W
Hi All, got a barn install to do. We want to put the inverter in another barn near the supply so we are looking at running the DC in SWA. I've...
Replies
0
Views
2K
W

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks