I'm rewiring a bungalow and currently the supply is a TT system and the meter and distributors switch is in a garage about 50 m from the bungalow.The supply up to the bungalow is currently wired in 10 mm SWA via a fused isolating switch.The owner is getting this system swapped to PME.If i wire from the meter to the isolating switch with 25mm tails,approx 1m,then away from the isolating switch in SWA up to the bungalow.Does the swa need to be RCD protected?It currently isn't.
 
Hi.

Just for clarification...do you intend installing a new SWA???

Dont forget, technically you will be exporting the PME form the garage to the bungalow, so theres that to think about.

As a rough calc I get a minimum of 25mm SWA as the max VD will be 3% (6.9V) due to the lighting circuits.
 
Yes i intend to install new SWA.Ialso calculated that 25mm would be needed due to the volt drop over that distance.My preference would be for the customer to get the distributor to move the meter and main fuse up to the house.I think he contacted them and for what they charge compared to the cost of the SWA and time for me to do it there was not a lot in it.
 
I agree, moving the meter to the bungalow is a better move, and if there isn't a lot in it then it's probably the way to go.

Maybe you could re-use the old 10mm SWA as a supply down to the garage, couple of sockets and a light for him.:D
 
Dont forget, technically you will be exporting the PME form the garage to the bungalow, so theres that to think about.

But will he?

Its a TT.

However, if there are no other services in the garage then i dont see it as being an equipotential zone.

But, if using 3 core 25mm submain to the house then the cpc will be adequate for the house and if there are services, main bonding could be done at the supply.

Am i right or am i right?

:D
 
Hi.

As a rough calc I get a minimum of 25mm SWA as the max VD will be 3% (6.9V) due to the lighting circuits.
would you not do calcs on the fact it is feeding a db then recalc for lighting circuits on a circuit by circuit basis as most db have a lighting cicuit and doing your way would rule out 5%
i may be missing something
 
VD is calculated from the origin of an installation in this case the garage so you must include the sub-main as part of it.


Quote from ECA...

Answer by the ECA: The overall voltage drop limit is 3% (6.9V) single-phase, if the sub-main is feeding lighting circuits.
 
Last edited by a moderator:
Thanks for all the replies very helpful.

However if the supply is swapped to PME, and due to the distance of the origin from the property,do you foresee this causing problems in reaching ZS,ZE readings? :confused:
 

Reply to Suuply main switch 50m from CU in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
833
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top