what if for instance there is a cpc in the SWA, at the DB end earth tag with fly lead connected to earth terminal. Other end metal socket. Is it a reportable fault if no SWA earth tag at this end?
 
No.
If for instance, you were keeping a PME earth separate from a TT earth, then the tag would only be used at the earthed end.
There are also 'earth nuts' which have a means to attach a fly lead.
It has often been argued that if the enclosure is metal, and any insulating paint/coating has been removed, then the tag and fly lead can be ommited.
However if the manufacturer's instructions stipulate the use of the tag and fly lead, then it should be used.
 
what if for instance there is a cpc in the SWA, at the DB end earth tag with fly lead connected to earth terminal. Other end metal socket. Is it a reportable fault if no SWA earth tag at this end?

I would report the fault and make arrangements to fix it at some convenient time. It is a departure from BS7671, but dont ask me the reg number.

Just read spins post, he knows more about it than me so go with his suggestions.
 
Last edited by a moderator:
yes i have used the earth nuts they are pretty good ,

But doing a PIR I noticed that on ring circuits run in SWA there are tags at the db ends but not at the sockets was not sure if its a fault
 
just to add, a banjo can be ommited if a threaded entry is used, and also if a serrated washer is used. there is no difference to earthing of SWA, than there is earthing conduit or MICC. i agree, that if glanding to a bare gland plate or trunking, then there isnt any need to use a banjo. you would have to ensure the locknut was very tight. this is my opinion.
 
At the end of the day, it boils down to what you consider to be safe or unsafe.
It can be argued that using the glands without banjos is no different to using brass bushes with conduit.
Although it can also be argued that the manufacturer's advise fitting them, and that SWA is flexible, so the glands are more likely to come loose.
 

Reply to Swa armour earthing in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

I think I've found the answers to my questions... I can just do a straight forward wiring i.e. connect the 3 wires from the armoured cable to...
Replies
7
Views
1K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
707

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top