Swa bonding, what method. | Page 2 | on ElectriciansForums
Discuss Swa bonding, what method. in the UK Electrical Forum area at ElectriciansForums.net
J
Jason Shawcross
Hi all
Just need your advice, theirs a discussion going on atm on site between a couple of sparks. We have around 50 apartments being fed by 3core swa from a panel room all glanded into the top of a run of trunking, armour isn't used as cpc. One spark is saying we need to run individual 16mm earth's to each gland
Another is saying 10mm to the first of each set and then looping. I would have thought just bonding the trunking near the board adding some bonding tags in-between the trunking sections and bolting the banjos on would suffice. Tbf the trunking is <o.o1 atm anyway to met. So what's your opinion and regs if possible, don't have book with me.
Thank you.
IF I understand correctly - the swa armour is not the cpc or the bonding conductor, but must be connected back to met so that it may act as cpc if required. So at least one connection to met and daisy chained with sufficient ccc to satisfy adiabatic is my thought. This may already be achieved by the trunking but your 10mm will surely do it?
There's isn't always a cavity to leave it
I know it can be difficult but most things are possible. Entry hole back of board, screw an adaptable box to the rear of it with no lid and use the lid fixing points to fit to the board, gland cable off at adaptable box. Easy peasy on paper and I am already visualizing it in my head:D
IF I understand correctly - the swa armour is not the cpc or the bonding conductor, but must be connected back to met so that it may act as cpc if required. So at least one connection to met and daisy chained with sufficient ccc to satisfy adiabatic is my thought. This may already be achieved by the trunking?
If it's not a cpc then it just requires supplementary bonding to earth
Good grief !:)
Here..I wouldn't class trunking as an accessory though.
[ElectriciansForums.net] Swa bonding, what method.
Na that's if you use conduit say as the cpc and you take a fly lead from the metal back box to the socket as the conduit is the cpc.
In this case the trunking is not acting as a cpc it mearly becomes an exposed conductive part because the swa is glanded to it.
exactly my thoughts or using 2core SWA and the armour as the CPC.
Reply to Swa bonding, what method. in the UK Electrical Forum area at ElectriciansForums.net
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...