I'm begining to understand some of your reasoning now. Not that i agree with much of what your saying here. I take it your working in the Jeddah area of Saudi, and English is not your first language. The installation is near, in Oman
Your current loadings seem basically fine. As are your IR readings, nothing wrong with those figures at all. Remember IR readings will differ with temperature, and if the original Ir readings were taken during the cooler months, you could well see a substantial difference than those taken in the summer months... I can well understand your predicament as regards to your plants continuous operation by the way!!!
Back to your trench, who the hell dreamt up that installation?? If were talking about a manufacturing plant that relies on these pumps and other equipment fed by cables in this trench, that are direct buried, someone has seriously got the installation method wrong!! All critical supply and feed cables should have been installed in a ducted system, like a buried multi storey concrete encased system that uses buried marshaling pit/rooms (can't think of the correct term, ...lol!!) Which then makes any of the installed cables ''rewirable/replacable'' Totally agree
When you say, ''de-rating factor for 5 cables is correct'' What are you talking about here, where did you get this 5 cables thing from?? Were talking about 48 cables in this trench are we not ?? Still totally in the dark on your reasoning of counting cable numbers instead of circuit numbers?? If you are using a current carrying capacity of 112A for a 70mm cable, and your load current is 110A then you will have a current carrying capacity of around 225A when ran in parallel. derating factor for 5 circuits on same trench is the factor taked in the original design. Ok, as you say we will count circuits. On same trench there are 20 circuits with 2 cables per phase and 8 circuits with 1 cable per phase. From this, the derating factor for only 5 circuits on same trench seems not correct. On manufacturers specifications I have seen until 12 circuits derating factor but no more. For this reason I'm looking for the sizing BS standard for these cables.
A couple of questions for you, ....What is the depth and width of this single trench?? bottom cables: 1.1m, top cables: 0,680m. There are not information about what circuits are on trench bottom, middle or top. Original design considered 0.8m for calculations. Width: 0.850m
You say that you have many ''water overflowings'' ..are you saying that this trench is continuously being flooded?? not continously but quite frequently
What de-rating factors have been applied to these cables. Grounf Temp: 35ºC, Soil Thermal Resist: 2.5ºC cm/w, Depth: 0,8m, Grouping: 5 circuits spaced 0.15m. Total derating factor: 0.5224. Derating factors taked for these conditions taked from manufacturer specifications.
What is the design ambient temperature your working too, ...i would have thought 50C, as that was the general standard of most installations when i worked in Saudi. 50ºC with 100% hum
You my friend are at a very real disadvantage, as you were not around during the laying down installation of these trench cables, so you have no idea of just how well (or not so well) this has be done. I hope that none of these cables sufferd any sheath damage during pulling in/laying in, if they are subject to all this on-going water flooding.... I have request by information, records, testing and other information about installation but nothing for the moment, only comments of plant people