Not got regs with me. Installing sub-main to detached garage using SWA method "D". Propose using 6mm 3 core SWA cable. From memory takes about 46/48amps. Don"t know about 17th regs..but in the 16th regs were you allowed to add 10% to the tabulated figure given if u/g. Basically I'm trying to find what is the max current that could be carried. The SWA cable will also installed within the house behind the ceiling/insulation. Thanks
 
Eh? Cable selection starts with working out how much current it needs to carry, you don't start with a cable size then work backwards to the current.

You can't apply any factors for part of the cable being underground if the rest of it is run through the ceiling void
The whole length of the cable should be rated according to the most onerous of the conditions it is to be installed in.
 
Hi Richard,
I'm just asking and not poking!

I take it you used .88 as the Ci and the cable is a 90degree? This being the best case, .51 being the worse case and would thus give a reading of only 21A !
Cg = 1, Ca = 1, Ci = .88, Cs = .9, Cc = .9 & Cd = 1 It =53A.

I was not doing a calculation just giving an idea of approximate value.

Cable run in insulation touching a wall surface is reference method A and 6mm² unarmoured multicore cable has a CCC of 32A, 90°C SWA has CCC of 42A.
70°C SWA generally has a slightly higher CCC than unarmoured multicore and slightly lower than 90° SWA so I went for about 38A.

Sorry not to be more technical:shame:
 
Eh? Cable selection starts with working out how much current it needs to carry, you don't start with a cable size then work backwards to the current.

You can't apply any factors for part of the cable being underground if the rest of it is run through the ceiling void
The whole length of the cable should be rated according to the most onerous of the conditions it is to be installed in.
Totally agree.
 
Hi Richard,
I'm just asking and not poking!

I take it you used .88 as the Ci and the cable is a 90degree? This being the best case, .51 being the worse case and would thus give a reading of only 21A !
Cg = 1, Ca = 1, Ci = .88, Cs = .9, Cc = .9 & Cd = 1 It =53A.

You can't use the 90degree ratings unless you have equipment designed for 90degree operation connected to both ends of the cable
 
Table 4D4A @ 70 degrees..states 46 amps Method D then it will be d/rating to suit environment. ie behind plaster board / insulation.
Consider each section of cable that has its own installation method independently, then calculate the current carrying capacity using the worst case scenario.

If it is installed to Method D then it is unlikley that there will be plasterboard and insulation underground, so consider the section underground and calculate the CCC for that.
Then consider the section in plasterboard and insulation (possibly method A) and calculate the CCC.

The lowest of the two values you get is the one that is limiting your installation design current.
 

Reply to SWA cable rating U/G in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
419
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top