martynb01132

Hi all looking for help on this one, if Im running SWA cables what is the minimum line size before I have to run a seprate earth, cheers Martyn
 
Its not as straight forward as giving a simple answer as it depends on cores as well as size meaning it dosnt follow a predictable path, im sure someone else can point you to the relevent table as i havent got it to hand.
 
Cheers I working for a company who insist we dont need to run a separate earth on any swa cable from 10mm upwards I think we do, generally the voltage is 400v 3 line supplies.
 
Cheers I working for a company who insist we dont need to run a separate earth on any swa cable from 10mm upwards I think we do, generally the voltage is 400v 3 line supplies.
i would question the kind of company you work for as they are clearly wrong in saying this you can work it out from the calculations in the regs as as i said before its size and core dependant but as you get to the larger swa cables then it becomes a requirement all the time im sure someone else will direct you to the table i spoke of.
Are you sure they didnt say 10mm or less?
 
the answer is in one of the NICEIC newsletters that are available from their site, I cant remember off hand but I think it was ok to use the armour as the CPC for line less than 6mm. Check the article though
 
Last edited:
i've seen some meaty swa's pulled in without a cpc to a point that i have had to question my own contractor manager whether a additional cpc should be pulled in. what he told me was they use the 'amtec' programme for the cable calc's. this could be used as a legal document if it ever went that far.
 
You can go a lot higher than that, just trying to find it on the web and if find it i will post it

Found it

steel wire armour as the earth conductor | GadSolutions,Electrical services,testing and excellence.

I think the csa of this tables refers to the steel, the copper equivilent is much smaller but can still be used.

From memory 70'C cable you are allright up to about 150 3 core and 400 4 core.

90'C cable is a bit more tricky, with 4 core ok up to 70mm but 3&2 core not so straight forward.

I will try and find something to post.

Try this from earthingnuts

http://www.earthingnuts.co.uk/pdf/pvc_xlpe.pdf
 
Last edited:

Reply to SWA cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
526
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
603
I am with you. Their RCD did not comply with the standard. The only one I know that does comply, though I am sure it isn't alone, is the Garo...
    • Like
Replies
10
Views
766

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top