eamonn1983

I need to work out if I will be required to run a separate protective conductor along side the swa cable I'm going to install. The cable is a sub mains feeding a 3 phase db panel in a large workshop. The cable is going to be a 50mm 4core 120 metres steel wire armoured installed in a underground duct. The protective device feeding the cable is a merlin gerin NS250N 160amp 3 phase mccb which and the readings at this end are zs 0.19 and pfc 1.23KA.

I'd be grateful if someone could tell me how I can determine if this needs a separate protective conductor and if so maybe explain the calculation,to help me,in the future.

Thanks in advance
 
a chart was posted the other day by eng54, showing the armour sizes required to comply as cpc. generally, all SWA cables up to 95mm, the armour is sufficient as cpc. use forum search and you should find it.
 
I need to work out if I will be required to run a separate protective conductor along side the swa cable I'm going to install. The cable is a sub mains feeding a 3 phase db panel in a large workshop. The cable is going to be a 50mm 4core 120 metres steel wire armoured installed in a underground duct. The protective device feeding the cable is a merlin gerin NS250N 160amp 3 phase mccb which and the readings at this end are zs 0.19 and pfc 1.23KA.

I'd be grateful if someone could tell me how I can determine if this needs a separate protective conductor and if so maybe explain the calculation,to help me,in the future.

Thanks in advance

The table i posted and is being referred too, does not imply compliance for bonding purposes, however, if this large workshop already has it's bonding requirements catered for, from the supply that this sub-main is being taken from, it's all well and good. However, if it were a supply for a stand alone workshop with extraneous services etc, then a full size separate earthing conductor would need to be installed alongside the SWA cable, unless of course you used a 5 core cable, which aren't easy to come by...lol!!
 

Reply to swa calculation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
349
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
895
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top