I know PV installers sometimes use SWA to carry DC into the house especially when the PV is ground mounted.

Can anyone help me understand the correct way of doing the following:
1) Earthing the SWA armour, should this just be connected to the house earth as it would for AC or something else, I have been told it can be left floating but would like to know if this is correct.
2) Assuming the voltage and current are within the cable spec is it OK to run 2 separate PV strings via a single run of 4 core SWA.

Thanks
 
It is NEVER ok to leave the armour of swa cable floating, it needs to be bonded to earth.
 
It is NEVER ok to leave the armour of swa cable floating, it needs to be bonded to earth.
Thanks James and just to be completely clear is this is definitely true for for SWA carrying DC ? If was for DC specifically that I was told it could float as apparently normal earth would provide no protection.
 
In my opinion 1. Earthing at the inverter for DC fault protection .
2. As long as the loads are balanced surely no different to 3Phase.
2. No need for any sort of balanced loads, just ensure the current is less than the cable rating for any core.
 
Thanks James and just to be completely clear is this is definitely true for for SWA carrying DC ? If was for DC specifically that I was told it could float as apparently normal earth would provide no protection.

Why would DC be any different to AC?

What would make a difference is whether or not the DC supply is connected to an earth reference or if it was an isolated supply.
 
Why would DC be any different to AC?

What would make a difference is whether or not the DC supply is connected to an earth reference or if it was an isolated supply.
The electrician that told me said that if the cable was damaged that the DC would probably arc and and that the earth connection would make no difference.

I asked the question here as I don't really understand it and I want to know the right way of doing it.
 
Are you sure they are an electrician as that sounds like they lack an understanding of some basic science.
Yes definitely an electrician and highly regarded at that, incidentally I am not an electrician but I have a science degree and I am not sure how this earthing would protect in this situation either.

I am happy to accept the guidance given here that SWA armour should always be earthed.
I understand that the inverter should be able to detect an imbalance and shut off.

BUT if it is daylight and the PV panels are producing power the cable will still be energised at a high voltage, assuming that the inverter has shutdown the voltage and current will be on the house earth but nothing will break the circuit and therefore there will be no protection. What am I missing here? this is why floating the armour as the electrician has said seemed sensible to me and its why I asked the question here.
 

Reply to SWA Carrying DC - Correct way to earth in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
456
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
931

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top