Is there any requirement or logic to using fire-retardant cable cleats for SWA inside a wooden shed?

There will be a 2 metre vertical run and a 3 metre horizontal run of 4mm 3 core SWA.
 
The regulations simply state that wiring systems shall be constructed to prevent premature collapse in the event of fire, there is no mention of type of installation....shed....domestic....commercial....industrial. Nor does it say common sense can be applied,it's a blanket requirement no matter how daft it might seem. Hence the disagrees to some of the above posts. If you ignore the requirement it's a departure, your call if you want to justify it on your EIC.

There's the answer, the wiring system will not collapse prematurely as the structure it is attached to will be in a state of collapse already by the time PVC cleats fail.

Also while no mention of the type of building, the intention is to prevent entanglement of emergency response personnel if they enter a building with a collapsed wiring system.

No firefighter is going to enter a shed other than to rescue a person and I can't recall there being a single case of shed based self immolation, so the whole discussion is moot.

Well it's mootier still as, in the infinitesimally small chance that a firefighter does enter and become entangled, who can prove what failed first and where.

This is so nonsensical I'm wondering if it's trolling?
 
There's the answer, the wiring system will not collapse prematurely as the structure it is attached to will be in a state of collapse already by the time PVC cleats fail.

Also while no mention of the type of building, the intention is to prevent entanglement of emergency response personnel if they enter a building with a collapsed wiring system.

No firefighter is going to enter a shed other than to rescue a person and I can't recall there being a single case of shed based self immolation, so the whole discussion is moot.

Well it's mootier still as, in the infinitesimally small chance that a firefighter does enter and become entangled, who can prove what failed first and where.

This is so nonsensical I'm wondering if it's trolling?
I understand entirely your point of view, but I disagree. I do not see any provision for the application of common sense or making a judgement in the regulation. If the reg was open to the installer making a judgement on whether it is required then there would be plenty of cases where it should be installed but wouldn't be. I'ts a blanket requirement.
 
I understand entirely your point of view, but I disagree. I do not see any provision for the application of common sense or making a judgement in the regulation. If the reg was open to the installer making a judgement on whether it is required then there would be plenty of cases where it should be installed but wouldn't be. I'ts a blanket requirement.

Few sparks haven't used some common sense from time to time regardless of the regs, just as not everyone drives at 30mph in a 30mph zone. I once knew someone that got up to almost 35mph in a 30mph zone, and it played on my mind for weeks after whether I should have reported him to the feds.
 
Last edited:
I understand entirely your point of view, but I disagree. I do not see any provision for the application of common sense or making a judgement in the regulation. If the reg was open to the installer making a judgement on whether it is required then there would be plenty of cases where it should be installed but wouldn't be. I'ts a blanket requirement.
And truth be told I'd probably use fire retardant clips but I'd be cussing like a sailor whilst doing it.
 
There's the answer, the wiring system will not collapse prematurely as the structure it is attached to will be in a state of collapse already by the time PVC cleats fail.

Also while no mention of the type of building, the intention is to prevent entanglement of emergency response personnel if they enter a building with a collapsed wiring system.

No firefighter is going to enter a shed other than to rescue a person and I can't recall there being a single case of shed based self immolation, so the whole discussion is moot.

Well it's mootier still as, in the infinitesimally small chance that a firefighter does enter and become entangled, who can prove what failed first and where.

This is so nonsensical I'm wondering if it's trolling?
Do the Regulations actually state the requirements for support methods are for the benefit of the emergency services.
 
The regulations simply state that wiring systems shall be constructed to prevent premature collapse in the event of fire, there is no mention of type of installation....shed....domestic....commercial....industrial. Nor does it say common sense can be applied,it's a blanket requirement no matter how daft it might seem. Hence the disagrees to some of the above posts. If you ignore the requirement it's a departure, your call if you want to justify it on your EIC.
It can never be a departure, a departure needs to have a degree of safety not less than the regulations.
 

Reply to SWA CLEATS IN WOODEN GARDEN SHED in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I hate it when a shed is TTd, why can they not be extended from the tn system? popcorn ready
Replies
7
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top