what is the current carrying capacity for 16mm 3 core swa with>100mm thermal insulation?b2 7671 0nly gives tables for ref method c d and e.
 
Agreed no direct table but looking at tables for other types seems to give a rating of 80% of 'clipped direct' rating so can only use 'rule of thumb' IMHO
 
i want to run an swa for a sub main of 80a ref method 101. looking like it will have to be in 25mm swa,would you go along with that sparx24???
 
Maybe an easy answer but may not be required, you say 3 core but if only running single phase then use table column 2 not 3.
Also use table 4E4A for xlpe if thats what you are using not 4D4A, lastly can the cable not be clipped above the insulation?
Going up to 25mm jumps the price a lot since it not 'booklet' size for pricing, although it will of course help Volt-drop/Zs readings.
 
Yes it is for twin and earth problem is there is no table for swa covered in insulation. Think I may just go 25 and have done with it better safe than sorry although stil no rating given for 25
 
Correct, 101 is Tw/e. also correct column 2 table 4E4A. You could argue & say ref method D, although this is buried in ground, temperature could be lower, but 90 degree C armoured, should be safe in insulation. You dont say length of run. I've got 3 core 16mm2 buried under my insulation & loft flooring run for 6 mtrs, had no warm / heat problems,although it was on top of insulation & has got good air circulation near eaves. piccollo
 
what is the current carrying capacity for 16mm 3 core swa with>100mm thermal insulation?b2 7671 0nly gives tables for ref method c d and e.

I had not realised initially that you were talking about depth of insulation, hence my previous post

I would rate it as clipped direct but de-rated by 50% because of the thermal insulation so table 4D4A - 89amps derated to approx 45A.
 
try AEI cable finder wizard.( google AEI Cables) i think 16mm is adequate. if XLPE.
 

Reply to SWA current capacity. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
667
Sounds more positive.
Replies
8
Views
629

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top