I've been asked to pick up a job where the previous builder went into liquidation and the property management company is asking me to complete the electrical works, relocate a fuseboard.

Everything the previous company has done is exceptionally neat but I'm concerned on the design front with the SWA, the supply from the mccb panel is 100A and the new swa they have pulled in is 16mm 4c (TPN) looking at the guides on the web current carrying capacity for this clipped direct is 94A, struggling to remember the exact formula would have to go through the books but is the 94A a guide and you can calculate it exactly?

Would rather not derate the mccb, and it's virtually impossible to rewire without taking ceilings down

Thanks
 
Hi - worst case is 3phase 70C rated then 16mm clipped direct is 77A, but if you are only using single phase of the cable it's 89A. If the cable is 90C rated then its 94A and 110A respectively. Hope that helps :)
 
Yep, that's the next hurdle ... sorry to say, but for a 100A supply I'd start with 25mm as min.
 
What your mac demand looking like taking diversity into account.? Id go with others and say derrating the mccb may be the way forward if the install could work off lower rated mccb
 
To be honest I wasn't aware you could just wind it down, having researched them a little I understand there is a pot on them which allows you to adjust the current setting

Thanks
 
To be honest I wasn't aware you could just wind it down, having researched them a little I understand there is a pot on them which allows you to adjust the current setting

Thanks

Then I'd suggest getting the advice of someone who knows what they are doing, there's usually adjustments on both magnetic and thermal tripping characteristics. You're outside the territory of plug and play fixed protection now.
 
Then I'd suggest getting the advice of someone who knows what they are doing, there's usually adjustments on both magnetic and thermal tripping characteristics. You're outside the territory of plug and play fixed protection now.

I see by your wonderful post that teaching people new things just isn't your style...
 

Reply to Swa current carrying capacity in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top