Morning All!

I have recently started work on a commercial site with a company installing air-con, the system that I have questions on is thus;


35mm2 4 core SWA as main supply to the board, where the armour is used as a CPC, which then feeds 10 x 3 phase circuits, supplied via 1.5mm2 4 core again using the armour as a CPC. All of these cables enter on the same plate of a metallic water proof box and then off to the board inside.


I have been asked to replicate the above system with the other identical 'pods', that have already been installed, which house the air-con coils etc. The way in which the other pod/system has been earthed, is with a 35mm2 main earth from the main supply SWA to the MET, and the outgoing circuit SWA's have not been individually earthed, but have 2 earth cables, with a nut and bolt, near each bunch of SWA's linking the armour up to the MET, but not via a banjo but with a nut and bolt in the metal box. The metallic box has
been bonded to the MET.

So, is this arrangement ok, as the armoured is being used as a CPC in all cables and the cables are all located on the same metal plate, in close proximity, this guarantees earth continuity?!? Or, as I suspect, should each outgoing SWA have its own earth connected to the MET?

Thanks for your time, I hope this makes sense!

Stuart
 
Stuart, this is quite common unfortunately and as long as there is continuity between the outgoing armour's and the met it should be fine, however, I would not be happy with this personally!
The outgoing armour's would be better fitted with brass banjo's on the inside of the D.B. and I normally bend the banjo upwards from the gland plate and link them all together with 6mm2 earth wire, with crimps and brass nuts/bolts/washers/spring washers. and then take a 6mm2 flying lead up to the MET thus giving a guarantee earth connection to all the outgoing armour's.
I also use this method for IP rated units as the last thing we want to do to water proof enclosures, is to drill the banjo onto the gland plate!!!
 
Thanks for the replies and advice,

The box I would say is painted steel, schneider IP rated metal box, if that helps?

...... If the SWA is individually earthed for the out going circuits, am I right in thinkng that 1.5mm2 will be fine, as the live conductors are this size?
 
Metal Box - Use serrated washers every time. Gives a good earth connection/continuity as well as extra protection of the glands working loose over time - especially with a clearance hole.
 
1.5 mm2 is already run as power, only about 3A per circuit so will be fine, I assume 1.5 mm2 is fine as cpc?
 
IMO the banjo's must always be used on the gland plate, except where glanding into threaded holes (eg besa boxes).
The correct method is to remove the paint from the gland plate before glanding, and to reinstate the protective coating afterwards (eg galv spray)
 

Reply to SWA earthing arrnagements in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

I hate it when a shed is TTd, why can they not be extended from the tn system? popcorn ready
Replies
7
Views
601
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
587
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
563
loz2754
L
  • Question
Not a reliable indication of a fault! What RCD characteristics (and also why is an incomer needed here)? Have you done a global L+N IR test to...
Replies
6
Views
746
  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks