Couple of questions. I’m at a job just now where the existing tails from the meter needed upgraded, they were 15m away from the fuse board & weren’t of an adequate size. The customer has already run a 3-core 25mm SWA to existing fuse board which will be upgraded to a 17th Edition consumer unit. Could do with a couple of bits of advice, first is regarding the termination of SWA at consumer unit. What’s the easiest & neatest way to do this? It’s a Wylex split load consumer unit he has bought. Looks like it may be a bit tight to fit gland straight to box & the earth won’t fit in the earth bar terminal. I’ve seen over the years different variations with gland attached to adaptable metal boxes but some are not the neatest. Also currently at the meter side there’s an old isolator, one of those with the big handles, what does this need to be replaced with to meet new regulations?
 
Best way would have been to use 16mm, but seeing as it's already in then you could use reducing pins.
If it's a bit tight to gland to then it is not really suitable. Glanding into a small chamber underneath won't really afford you any more space as the supply conductors have to enter the unit some way.
What is wrong with the isolator regarding current regulations ?
 
Couple of questions. I’m at a job just now where the existing tails from the meter needed upgraded, they were 15m away from the fuse board & weren’t of an adequate size. The customer has already run a 3-core 25mm SWA to existing fuse board which will be upgraded to a 17th Edition consumer unit. Could do with a couple of bits of advice, first is regarding the termination of SWA at consumer unit. What’s the easiest & neatest way to do this? It’s a Wylex split load consumer unit he has bought. Looks like it may be a bit tight to fit gland straight to box & the earth won’t fit in the earth bar terminal. I’ve seen over the years different variations with gland attached to adaptable metal boxes but some are not the neatest. Also currently at the meter side there’s an old isolator, one of those with the big handles, what does this need to be replaced with to meet new regulations?
The SWA pulled in already, does that mean they have installed aSWAwith an extra conductor, or are they intending to use the armouring as the earth?
 

Reply to SWA main supply questions. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
701
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
577
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top