A

Adam Smith

Hello all,

I am running a distribution circuit to a sectioned off part of someone's house, I'm going to be running the cable under the wooden floor and dropping down in to the room from above. I can use either 10mm SWA or 16mm T&E to achieve this but was just wondering what people think would be the easiest cable to try and pull through joists and what not?. I assume neither option is going to be huge laugh!

Thanks
 
I don't see the problem. 10mm² 3 core SWA is less than 20mm diameter. Holes in joists can be up to 0.25 x joist depth without further calculation . So, say 8" joists, 2" holes; more than twice the diameter of the cable. No problem, although easier with a mate or two, as davesparks says.
 
10mm 3 core? I thoughtit was fairly hefty! The whole needs to be larger than the cable too surely by at LEAST 5mm, my drill and hole cutter dont fully fit inbetween most joists either so the holes are drilled at an angleid be avoiding pulling a swa in myself!
 
Hello all,

I am running a distribution circuit to a sectioned off part of someone's house, I'm going to be running the cable under the wooden floor and dropping down in to the room from above. I can use either 10mm SWA or 16mm T&E to achieve this but was just wondering what people think would be the easiest cable to try and pull through joists and what not?. I assume neither option is going to be huge laugh!

Thanks

obviously im unsure of the situation and design. but does the cable have to be so big in the first instance. i'm guessing the incomer is single phase 100amp?
 
When drilling holes in 10" floor joist on new builds, I cut a bit of scaffold board about 300mm long mark my holes on it and drill my holes then I measure off the wall where holes are going to be,ping a chalk line from one side to the other then I can line the edge of the scaffold board up with the chalk line mark the holes on every joist and every hole is in a perfect line. Makes 1st fixing so much more of a doddle when it all lines up perfectly.

I hate new builds with engineered floor joists with the knock outs in, as they rarely line up.
 
When drilling holes in 10" floor joist on new builds, I cut a bit of scaffold board about 300mm long mark my holes on it and drill my holes then I measure off the wall where holes are going to be,ping a chalk line from one side to the other then I can line the edge of the scaffold board up with the chalk line mark the holes on every joist and every hole is in a perfect line. Makes 1st fixing so much more of a doddle when it all lines up perfectly.

I hate new builds with engineered floor joists with the knock outs in, as they rarely line up.

When dealing with those damned I joist thing it's always worth speaking to the structural engineer, we have always got permission (written) to drill them where they don't line up. The usual answer we got was to drill no larger than the knockouts and no more holes to be made than the number of knockouts available.
 
When dealing with those damned I joist thing it's always worth speaking to the structural engineer, we have always got permission (written) to drill them where they don't line up. The usual answer we got was to drill no larger than the knockouts and no more holes to be made than the number of knockouts available.

Same here we've got permission before to drill them where they don't line up. I have also done a job before where they would have none of it and made us use only the knockouts, it was a complete pain in the neck and it looked a bit rough lol.
 
Last edited:
Same here we've got permission before to drill them where they don't line up. I have also done a job before where they would have none of it and made us use only the knockouts, it was a complete pain in the neck at it looked a bit rough lol.
usually these i beams have holes at the top and the next ones been fitted upside down so they are at the bottom. nice!
16mm T&E will be slightly easier to pull in compared to swa/hituff(how very dare you to suggest such a beast)
its all do able with bit of judicious planning first mind
seems to me that this house bashing is not for the faint hearted:grin:
keep the holes straight ,use a cable reeler if possible to avoid kinks and use at least 2 of you
i have every faith in you OP
 
Sadly I haven't had a friend to pull cables with for a number of years now! The chap who owns the house is a plumber so I'm sure he can offer some assistance (could heat the cable up with his blow torch to make it more compliant!)
 

Reply to SWA or T&E??? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Does it really actually need earth sleeving inside the tube? I know it feels a bit bodgy but what's going to happen and isn't an unbroken...
Replies
9
Views
606
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
515

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top