BAD idea. Without going into huge amounts of scientific detail, this way of doing it will induce current into the armour/earth and potentially create excessive heat at the termination ends (assuming the cables are terminated into a steel enclosure of some sort). This idea needs binning off and so does the electrician that proposed it because he hasn't a clue what he's doing!

i know what i wanted to say, but didn't know how to say it. Cheers…………..Howard
 
You're going to run into voltage drop problems, especially if you put a heater or two on in the cold weather.

Not much more than 12A per 4mm² cable to drop 5% over that distance.
 

Reply to SWA problem in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

Sounds more positive.
Replies
8
Views
613

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top