This isn't for central heating really this is for a project
Can I switch a 2 port valve like bellow .I.e is the "Switch line" 230v?

MCB >>> Junction box >> Line, Neutral, Earth >>> 2 port valve
........................................>> Line split to Light Switch >>> Connected to SL/Orange of 2 port valve.
 
If you mean a normal spring-return central heating valve like the Honeywell V4043, yes, the control input is 230V, it's just a small 230V motor. Note the colour code though; 230V on brown and blue opens the valve. Once open, the internal microswitch connects grey and orange together. There is no need for a permanent line feed unless you are using the microswitch to trigger something else, in which case PL goes in on grey and the valve will make orange live once open.
 
Just connecting Brown and Blue to a plug will open the valve?

Yes. (and earth, preferably!)

Orange is the switched line out of the valve that normally controls the boiler / pump. The valve energises the orange when it is fully open, like a relay. When multiple valves / zones are in use, all the orange leads are paralleled so that when any valve opens, the system fires up. The brown control inputs that open the valves in the first place remain separate.
 

Reply to Switch 2 port Valve with Light Switch...........for project only in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

B
  • Article
Replace central heating gate valve with 2-port valve My house has a separate central heating loop that heats an annex. The annex loop has 3 x...
Replies
0
Views
299
Barnjet
B
It could be a slave switch where you would have a L in and a common wire out to a master switch.
Replies
3
Views
595

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top