Reg 701.512.3 states :
In Zone 0 : Switchgear or accessories shall not be installed
In Zone 1 : Only switches of SELV circuits supplied at a nominal voltage not exceeding 12V a.c rms or 30V ripple-free d.c shall be installed, the safety source being installed outside zones 0, 1 or 2
In Zone 2 : Switchgear, accessories incorporating switches or socket outlets shall not be installed with the exception of
(i) switches and socket-outlets of SELV circuits, the safety source being installed outside zones 0, 1 or 2 and
(ii) shaver supply units complying with BS EN 61558-2-5
Except for SELV socket-outlets complying with Section 414 and shaver supply units complying with
BS EN 61558-2-5,
socket outlets are prohibited within a distance of 3m horizontally from the boundary of zone 1
They clearly state socket-outlets, I think if they were referring to socket-outlets, switches etc. in general, they would have stated swich gear, control gear or accessories.
I might be wrong, but that is how I interperet the Regs.
Regards
Mark