It has recently been pointed out to me that EN 60335-1 section 24.2 that switches cannot be used in flexible cords. Why then can I buy a table lamp from a major UK store with a switch in the cord? Are there exceptions to the rule?
Quote:
24.2
Quote:
24.2
Appliances shall not be fitted with
– switches or automatic controls in flexible cords;
– devices that cause the
protective device in the fixed wiring to operate in the event of a fault in the appliance;
– thermal cut-outs that can be reset by a soldering operation.
NOTE The use of solder having a melting point at least 230 °C is allowed.
Compliance is checked by inspection.