P

Piratepete

Evening All!
I notice that some folks recommend the MEM KMF 800 or 600 for an 80 amp or 60 amp switch fuse between the meter and a distant consumer unit.

I think it only has a single pole switch. Is there any requirement for it to be double pole? Where is it specified?

Cheers
 
Depends what the earthing arrangements are. TT would require DP, whereas TN-C-S wouldn't matter as the earth would still be connected. Have a look at Regulation 537.1.2.
 
Taking this further, should I be using dp switched sockets on TT installations? 537.2.2.1 seems to suggest it. It would seem that the cb in your normal consumer unit would not be sufficient nor a sp light switch.
 
i think KMF's are DP?

Also, TT systems require DP isolation, which is in the form of the CU main switch.

Yes, as Jason said, a 'linked' double pole main switch will satisfy 537.2.2.1 the requirement does not need to extend to accessories etc.
 
My understanding, is that DP is required for isolation only.
With socket-outlets, functional switching is provided by the switch, isolation by removing the plug.
With SFCU and lighy switches, the switch is functional and thw Main switch at the CU provides isolation, unless DP MCBs or RCBOs are used.
 
Interesting! Some sockets have dp switching such as MK Logic Plus, but loads don't and you wouldn't know without testing them! I've never seen dp MCBs in a domestic installation. So we have these nice kits for locking circuit breakers (for isolation?). But, I think you're right - there is an addendum to the Regs for the Isolation column of Table 53.2 which states that for TT isolation requires disconnection of all the live conductors.

So on TT installations - be aware!
 
I'm not sure from your 'be aware' advice whether you still believe sockets have to be double pole on TT supplies?

A double pole main switch satisfies the requirements of 537.2.2.1
 

Reply to Switchfuse - SP or DP? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
A microwave isn’t on for long lengths of time. That’s the point of a microwave. Being a combi, it might be on for longer… but not at its full...
Replies
2
Views
984
D
  • Question
The revised arrangement - please check that I have fully understood the points made in the above threads. Obviously a qualified electrician will...
Replies
5
Views
3K
Deleted member 155212
D
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
2K
Deleted member 155212
D
Thanks for your feed back re- G99 SGI paper work i be file again. SSEN G99 SGI-1 fasttrack
Replies
5
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks