5 core SY cable - 3 phase circuit (neutral not used) would the de-rating factor apply, as obviously only 3 cores are carrying current!

In my case I've got 4mm/5c handy and the machine is rated at 34A.
 
Id treat it as its core no' (5), the rating of the cable isnt so simple to work out if the core is their but not used it still ocuppies space altering the effective surface area the other conductors have against the outer-sheath, id get 6mm but be careful here although Elland cables supply a good proportion of the cable near me as its just down the road other manufacturers exist and may differ as they have variations with regards to braiding and sheathing thickness.
And to note the 4mm 5core is rated at 34amps and subject to manu' spec derating of 0.75, a 6mm will only leave you with a 33amp rating without other factors taken into account so loading characteristics of machine might be needed to be taken into account but if running at 34 amps then 10mm may be your choice.
 
Last edited by a moderator:
I understand what you say but, at worst it would be 4 core still with no factor to apply as the CPC is never included, ie, 2 core for SP & 4 core for TP as per BS 7671.
Good point made but although i have every confidence in you id be inclined to check with manufacturer with this one but know what your saying, im used to saying 5core when i get 4core and earth and ive always got the core im after.
 

Reply to SY Cable - current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

They do a cy type with pur coating and it is even tougher but is shielded
Replies
3
Views
400
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
667

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top