Hi all i am in the process of doing a pir on a residential home and they have some 3phase sockets wired in 4 core sy flex using the cpc as the neutral and the sy flex " armour" as the cpc. Obviously im going to fail the circuits for using the cpc as the Neutral but just wondering about the armour/cpc. As on sy flex its more of a braiding than a proper armour

Cheers
 
Firstly the CPC should never be used as a live conductor , and also on an SY flex the armour is no way good enought for a CPC this should be used as protection only , you are 100% correct ,these cables should be changed and a cable with the correct number of required cores used
 
Thank you this is what i thought the circiut was installed in 2004 and has had a pir done since by another company and was not picked up
 
Also to note is the braiding must be earthed too but not used as mentioned above as a functional earth, the no' of times ive seen it utilised as an abrasion resistance without it been earthed is unbelievable, to be noted also its original design is as a screening for interference which would normally be grounded but years on the market have found it been used for other jobs which i dont see an issue but as long as it is installed correctly and safely and this is where many fail. I have also seen it used on exterior jobs and if i recall the manufacturers say it is not to be used for outside installations.
 
Also to note is the braiding must be earthed too but not used as mentioned above as a functional earth, the no' of times ive seen it utilised as an abrasion resistance without it been earthed is unbelievable, to be noted also its original design is as a screening for interference which would normally be grounded but years on the market have found it been used for other jobs which i dont see an issue but as long as it is installed correctly and safely and this is where many fail. I have also seen it used on exterior jobs and if i recall the manufacturers say it is not to be used for outside installations.

!00 % agree screening couldnt for the life of me remember the word ,lol , thanks for filling in the bits id missed
 
Also to note is the braiding must be earthed too but not used as mentioned above as a functional earth, the no' of times ive seen it utilised as an abrasion resistance without it been earthed is unbelievable, to be noted also its original design is as a screening for interference which would normally be grounded but years on the market have found it been used for other jobs which i dont see an issue but as long as it is installed correctly and safely and this is where many fail. I have also seen it used on exterior jobs and if i recall the manufacturers say it is not to be used for outside installations.

The steel braid of SY cable was never intended to be used as a screen, it's just a mechanical protection and to blow fuses when cable gets damaged (when steel braid is earthed). If you want screening for interference then you have a CY cable with tinned copper braid which must be used with a 360 degree connection glands. For additional mechanical protection it can be used with plastic or metallic flexible conduits.
 
Last edited:
We have another active thread on the go discussing this subject sysrq as I see you have found and as this is many years old, I will close this one.
 

Reply to Sy flex armour used as cpc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
763
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
765

Similar threads

totally agree
Replies
12
Views
1K
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
889

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top